Alarm_H VAR Bit
Alarm_L Var Bit
Owout DQ, 1, [$CC, $EC]
Owin DQ, 1, [Alarm_H, Alarm_L]
Is it going to send back a 1 or 0 alarm bit?
Think so
How's this?
Alarm_H VAR Bit
Alarm_L Var Bit
Owout DQ, 1, [$CC, $EC]
Owin DQ, 1, [Alarm_H, Alarm_L]
Is it going to send back a 1 or 0 alarm bit?
Well, not so good.
There is only 1 Alarm status bit, No SkipROM, and mode 4 (bit data) is used to retrieve it after the AlarmSearch command.
If there is an alarm, you have to read the temperature to figure out whether it's too high or too low.Code:Alarm VAR BIT OWOUT DQ, 1, [$EC] OWIN DQ, 4, [Alarm]
It will return a 0 if there is an alarm, 1 if not. But you can reverse that easily with...hth,Code:Alarm = Alarm ^ 1
DT
Thanks Darrell
I see. I forgot to change the mode bit. Still learning.
I really need a setpoint temperature for the "smarter" HVAC thermistat I am working on. I think I will just use another 18B20 as my setpoint temp and not worry about the alarms.
Absolutely
I am entering a setpoint in the software and also going to have another 18B20 outside to give me the "variable setpoint". This way the system knows if it really needs to turn on or to just pause until it warms up or cools down