Read 65.xxxx
Does Not Update Hold Sensor And Nothing Changes
Reloaded Several Programs And They Work However Still Get Low Tmp Reading
Dont Think Its A Hardware Problem Because It Works Perfectly In Mikroe
Guess I Could That But Have Better Luck With Pbp As For As Adding My Stuff
65.xxx
Hmmm....maybe 65.535? 65.535 F? 65.535 C ?
Ever think that maybe your input was all 1's? And that it might've just been coincidence that your temp's are about 30 degrees low depending on the temp of the room?
Try this, might help...
http://www.picbasic.co.uk/forum/showthread.php?t=561
AND:
Last edited by skimask; - 23rd July 2008 at 20:05.
Hi, Cleaver
I suppose you work on an easyPic 4 or 5 ...
try this with sensor connected to PORTE2 and Pullup on porta.0 and 1.
After power on, type of sensor and ID is displayed.
press RA0 Button ( active low ! ) and you turn to thermo mode ( thermostat, in fact , see RA0 and RA.1 use ... )
Alain
PS : Fully PbP Written Program...
Last edited by Acetronics2; - 23rd July 2008 at 21:03.
************************************************** ***********************
Why insist on using 32 Bits when you're not even able to deal with the first 8 ones ??? ehhhhhh ...
************************************************** ***********************
IF there is the word "Problem" in your question ...
certainly the answer is " RTFM " or " RTFDataSheet " !!!
*****************************************
jcleaver
Here is a couple of files for you to play with.
pbptc.txt is your program that correctly displays the temp C and changes when the temp changes. You will need to change the LCD port, I use an easypic5 and you are using a different port.
I also have a program for MikroB attached, again it is for the ep5 board.
Take a few minutes and look at how the temp is being read in both. Once you figure that out you will see where the problem is.
BTW the formula is from the DS18S20 datasheet.
In your Mikro file did you notice that the temp was calculated before it is converted?
if j2 = $FF then
tmp_sign = "-" ' temperature sign
j1= j1 or $FF ' complement of two
j1= j1 + $01
else
tmp_sign = "+"
end if
j2 = (j1 and $01) * 5 ' Get decimal value
j1 = j1 >> 1 ' Get temp value
j1 = ((j1*9/5)+32) 'Convert C to F
And in your PBP file nothing is calculated until after the conversion.
TEMP = ((TEMP*9/5)+32 )
Lcdout $fe, 1, dec (temp >> 1),".",dec(temp.0 * 5)," degrees C"
Good Luck!
Acetronics: May I play around with the thermostat program you posted?
Last edited by manwolf; - 23rd July 2008 at 23:18. Reason: Brain Bubble
Want To Thank All Of You For Your Help Been Great To Work With
Will Keep You Updated
Also Would Like To Look At The Pb Code For The Thermostat Program
If Not Giving Away Something
Again Thanks
Jack
Manwolf
Worked With Your Pbp And Your Right It Is Displaying The Correct C Temperature
Its Pb Math Thats Incorect
Any Ideas How ?
Also The Formula Temp = ((temp*1.8)+32) Gives Corect Answer But Wont Compile
On Pbp