I considered a DS1820 but was concerned about the 1-wire network immunity to noise... I want to have at least 5 temperature sensors 3 indoor, two of which will be up to 200 feet from the PIC probably running along side Romex 120v AC lines. An outdoor sensor and a sensor in a thermowell in a boiler ~180 Deg.F. Thermistors are industry standard in a boiler so I didn't want to reinvent the wheel. And as for the longer runs I just figured the thermistor lines could be filtered with some caps since they're DC so noise would be less of a problem. I guess adding a buffer will provide a more robust signal. Thanks... I'll look into it a bit more now that I know what to look for.
Last edited by Neosec; - 1st June 2008 at 01:39. Reason: grammer
I have successfully used the Microchip MPC9701. Since it has an analog output, you can run the signal 50' or more. Just use a low-pass filter (2K in series, .1uF to GND) with the A/D input and average 16 samples with a 1mSec delay between samples (so that you average out over one complete cycle of 60Hz). The output is linear with temperature (unlike thermistors), and doesn't need calibration. Cheap, too.
Charles Linquist
LM34 or LM35 will work too. A cap from signal to ground for longer distances and good to go.
Like the Microchip MPC9701 these are also linear. Your harsh environment is not a problem. Good for around 300 F.
Industry standard? I use the LM34 in thermo wells at the plant where I work. One has an average temp 250 F. One degree resolution, no problems. We must be Non- standard.
Lots of options.
Dave