YHDC current sensor - the theory please


+ Reply to Thread
Results 1 to 24 of 24
  1. #1
    Join Date
    Aug 2006
    Location
    SWITZERLAND (french speaking)
    Posts
    952

    Default YHDC current sensor - the theory please

    Hi All,

    I'm resuming a project I started more than one year ago; it is about to use a YHDC current sensor.

    Name:  YHDC small.jpg
Views: 317
Size:  7.0 KB


    For now, I have a 16F18446 carrying a 12 bits ADC that I hope sufficient just to put me on the track and avoid the usage of an external higher resolution ADC chip adding "difficulties".

    The YHDC sensor I have on my bench is a 100A:50mA model.

    I found a lot of these drawings like this one below but I can't make them work or better said, I don't know how to "read" their output.

    Name:  ARDUINO.jpg
Views: 205
Size:  21.1 KB



    Do I have to sample let's say a 30 to 50 times or so to grab an alternance, find out both zero-crossing values (or as close as possible) and then extract the higher value in between?

    What is the correct way to do this?

    Thanks for any explanation on this one
    Attached Files Attached Files
    Roger

  2. #2
    Join Date
    Nov 2005
    Location
    Bombay, India
    Posts
    971


    Did you find this post helpful? Yes | No

    Default Re: YHDC current sensor - the theory please

    If you are trying to read the magnitude of current flowing in the primary of the current transformer(CT), you would like to first amplify the AC output of CT using an op-amp. Then do a DC peak conversion on the output of the op-amp. Read this value. It will be proportional to the current flowing in the primary. The ADC on the PIC can now read this DC value in a poll.

  3. #3
    Join Date
    May 2013
    Location
    australia
    Posts
    2,705


    Did you find this post helpful? Yes | No

    Default Re: YHDC current sensor - the theory please

    a simple digital peak detector will give a reasonable result,

    eg
    2v p-p input offset to approx 1.5v for a vcc of 3.3v for adc

    Name:  RigolDS0.jpg
Views: 179
Size:  160.1 KB


    [arduino ide serial plotter]
    at a 200us sample rate
    Name:  peak200.jpg
Views: 191
Size:  107.3 KB

    at 1000us sample rate , its still not bad
    Name:  peak1000.jpg
Views: 187
Size:  139.7 KB


    Code:
    '****************************************************************'*  Name    : peak_detector_ADC_16F18446.pbp
    '*  Author  : richard
    '*  Notice  : 
    '*          : All Rights Reserved
    '*  Date    : 
    '*  Version : 1.0
    '*  Notes   :
    
    
    
    
    
    
    
    
     '====== PIC 16F18446 FUSES ========================================================================
      #CONFIG
        __config _CONFIG1, _FEXTOSC_OFF & _RSTOSC_HFINT32 & _CLKOUTEN_OFF & _CSWEN_ON & _FCMEN_ON
        __config _CONFIG2, _MCLRE_ON & _PWRTS_PWRT_64 & _LPBOREN_OFF & _BOREN_SBOREN & _BORV_LO & _ZCDDIS_OFF & _PPS1WAY_OFF & _STVREN_ON
        __config _CONFIG3, _WDTCPS_WDTCPS_31 & _WDTE_SWDTEN & _WDTCWS_WDTCWS_7 & _WDTCCS_LFINTOSC
        __config _CONFIG4, _BBSIZE_BB512 & _BBEN_OFF & _SAFEN_OFF & _WRTAPP_OFF & _WRTB_OFF & _WRTC_OFF & _WRTD_OFF & _WRTSAF_OFF & _LVP_OFF
        __config _CONFIG5, _CP_OFF
      #ENDCONFIG 
    
    
    ' ====== REGISTERS =================================================================================
    
    
        ANSELA  = % 00100000
        ANSELC  = % 00000000
        TRISC   = % 11101111
        ADCON0  = % 10000100 'ADC is ON, RIGHT justified result 
    
    
    ' ====== DEFINES ===================================================================================
        DEFINE OSC 32
        DEFINE ADC_BITS 12     'Number of bits in ADCIN result
        DEFINE HSER_TXSTA 24h ' Enable transmit, BRGH = 1
        DEFINE HSER_CLROERR 1 ' Clear overflow automatically
        'DEFINE HSER_SPBRG 138 ' 57600 Baud @ 32MHz, -0.08%
        DEFINE HSER_SPBRG 68  ' 115200 Baud @ 32MHz, 0.64%
        SP1BRGH = 0
        BAUDCON.3 = 1         ' Enable 16 bit baudrate generator
        pause 500
        RC3PPS = 15          ;tx            PORTC.3 
        RA0PPS = 15          ;tx            PORTA.0      ;PK3
        RC4PPS = 0           ;rx            unused
        LED    VAR LATC.4
        clear
        new_read     var word
        State        Var BYTE 'serial Bd (baud per second)
        peak         var word
        last         var word
    
    
    ' ====== setup PROGRAM =============================================================================
        led = 1
        ADCIN 5, last  
        pause 1000
        HSEROUT ["ready ",13,10]
        led = 0    
         ;707 -3670
    ' ====== MAIN PROGRAM =============================================================================
    MAIN:
        ADCIN 5, new_read ' ADC 
        gosub getpeak
        HSerout ["ADC:",dEC new_read,",peak:",dEC peak,13,10]                    '    PLOTTER
        pauseus 200   ;   sample rate                         
    GOTO MAIN
    
    
    getpeak:
        if state==0 then    ;rising
           if   new_read < last  then
            state = 1;falling 
            peak =   last
           endif
        else        ;falling
           if   new_read > last   then 
            state = 0;rising 
            peak =   last
           endif
        ENDif
        last = new_read
    return
    Warning I'm not a teacher

  4. #4
    Join Date
    Aug 2006
    Location
    SWITZERLAND (french speaking)
    Posts
    952


    Did you find this post helpful? Yes | No

    Default YHDC current sensor - the theory please

    Peak detector! That's it!

    Thanks a lot for explaining and the code I can't wait to try when I'm back from office

    Though, why do I always read about 3.3V measuring circuits and not 5V?

    Also, a "peak detector" can be as simple as a resistor and a capacitor in parallel "smoothing" the output of the sensor, or like Jerson wrote, of the op-amp, right?

    If "yes", how do I dimension them? Are trials and readouts on the scope the best way to go?
    Roger

  5. #5
    Join Date
    May 2013
    Location
    australia
    Posts
    2,705


    Did you find this post helpful? Yes | No

    Default Re: YHDC current sensor - the theory please

    why do I always read about 3.3V measuring circuits and not 5V?
    my dev board has a 3.3v reg, otherwise can't see that it makes a difference


    a "peak detector" can be as simple as a resistor and a capacitor in parallel "smoothing" the output of the sensor, or like Jerson wrote, of the op-amp, right?
    not really , it needs a rectifier too. if the wave is not symmetrical the neg and pos peaks may be needed. plus it still needs adc code to read it in anyway


    Are trials and readouts on the scope the best way to go?
    almost essential, especially depending on the nature of the current being monitored,
    if the current is not sinusoidal and/or varies rapidly then its going to need filtering and other compensation to get any sort of reasonable calibration
    Warning I'm not a teacher

  6. #6
    Join Date
    Aug 2006
    Location
    SWITZERLAND (french speaking)
    Posts
    952


    Did you find this post helpful? Yes | No

    Default Re: YHDC current sensor - the theory please

    a "peak detector" can be as simple as a resistor and a capacitor in parallel "smoothing" the output of the sensor, or like Jerson wrote, of the op-amp, right?
    not really , it needs a rectifier too. if the wave is not symmetrical the neg and pos peaks may be needed. plus it still needs adc code to read it in anyway
    May I kindly ask for a principle circuit to start with the correct foot please?

    I don't see how to "rectify" a very low AC signal - I'm an electrician and used to easely handle voltages over 230VAC but when it comes down to millivolts.... 😬
    Roger

  7. #7
    Join Date
    May 2013
    Location
    australia
    Posts
    2,705


    Did you find this post helpful? Yes | No

    Default Re: YHDC current sensor - the theory please

    Why do want a nasty old analogue peak detector, When you can create a digital one as per my code ?
    Using the very cct you posted.
    If you realy need to try analogue google ""peak detector circuit"



    An accurate analogue peak detector uses an opamp to create an "ideal" diode [overcome the diodes vf ]
    Warning I'm not a teacher

  8. #8
    Join Date
    Aug 2006
    Location
    SWITZERLAND (french speaking)
    Posts
    952


    Did you find this post helpful? Yes | No

    Default YHDC current sensor - the theory please

    ...sorry Richard, didn't try your code by now - still in office.... 😬
    Roger

  9. #9
    Join Date
    Aug 2006
    Location
    SWITZERLAND (french speaking)
    Posts
    952


    Did you find this post helpful? Yes | No

    Default YHDC current sensor - the theory please

    Richard,

    I've connected my YHDC sensor one pin to ground and the other to RA5. Got readings (see hereunder).

    Because I'm not sure what I'm doing right now with the current sensor, I tried to add a 1Mohms resistor and a 100nF polarized cap between GND and RA5. Same readings.

    Just for info, my multimeter shows 0.157mVAC - I'm measuring a 230VAC 42W light bulb for now.

    I get readings on my serial monitor but the values don't make too much sense to me, for now - there's going to be some kinf of scaling to do, no?


    This is what I get for now with bulb "ON":
    Name:  Readings.jpg
Views: 175
Size:  36.9 KB


    And bulb "OFF":
    Name:  Bulb OFF.jpg
Views: 175
Size:  26.8 KB
    Roger

  10. #10
    Join Date
    May 2013
    Location
    australia
    Posts
    2,705


    Did you find this post helpful? Yes | No

    Default Re: YHDC current sensor - the theory please

    It can't work wired the way you described. The ac signal must be biased by vcc/2 and be less than vcc peak to peak.
    If the serial baud rate is too low it will ruin the sample rate.
    If the burden resistance is incorrect extremely high voltage may be possible

    Post code and schematic
    Last edited by richard; - 1st December 2025 at 22:14.
    Warning I'm not a teacher

  11. #11
    Join Date
    Oct 2005
    Location
    Sweden
    Posts
    3,624


    Did you find this post helpful? Yes | No

    Default Re: YHDC current sensor - the theory please

    Have you connected your CT as shown in your first post? That is, the bottom to 2.5V (or VRef/2) and the top to input pin AND - VERY IMPORTANT - a load resistor shown as 33ohms in diagram? You must have a load resistor or the output voltage across the secondary of the CT can get very high, possibly damaging the ADC input.

    Then, your CT produces 50mA with a 100A primary current. 1A primary give 0.5mA and so yout 42W load gives about 100uA secondary current. Keep that in mind when selecting the load resistor.

    EDIT: OK, Richard beat me to it while I was typing.

  12. #12
    Join Date
    Aug 2011
    Posts
    460


    Did you find this post helpful? Yes | No

    Default Re: YHDC current sensor - the theory please

    You might want to specify the model number of the sensor since there are a number of different types, and the circuit shown may not even apply

  13. #13


    Did you find this post helpful? Yes | No

    Default Re: YHDC current sensor - the theory please

    adjust resister to for the mid current used incase of some nonlinearity... shotkey diode has .3 volt drop
    Name:  ct.JPG
Views: 165
Size:  41.8 KB

  14. #14
    Join Date
    Aug 2006
    Location
    SWITZERLAND (french speaking)
    Posts
    952


    Did you find this post helpful? Yes | No

    Default Re: YHDC current sensor - the theory please

    Sorry guys for not reponding earlier - I'm still waiting for 20A:50mA current sensor to arrive; my 100A:50mA are far too low and "out of range" for what I intend to measure.

    BUT I could grab a 5A:1V one from a friend today so I'm back on my workbench.

    To have "better" values -measures with FLUKE 177- , I now use my 230VAC hairdryer:
    Pos 1: fan only = YHDC:54mVAC - FLUKE: 1.1A
    Pos 2: fan + low heating = YHDC: 170mVAC - FLUKE: 3.5A
    Pos 3: fan + high heating = YHDC: 320mVAC - FLUKE: 6.6A


    Since I now use a voltage output type sensor, I leave the burden resistor out, right?

    Name:  YHDC_500.jpg
Views: 155
Size:  15.9 KB


    And here are my readings:

    OFF:
    Name:  Haidryer_OFF.jpg
Views: 149
Size:  45.2 KB


    Pos 1:
    Name:  Hairdryer_1.jpg
Views: 152
Size:  46.4 KB


    Pos 2:
    Name:  HairDryer_2.jpg
Views: 150
Size:  45.0 KB


    Pos 3:
    Name:  Hairdryer_3.jpg
Views: 151
Size:  46.4 KB


    I can't still figure out what I'm reading.
    Last edited by flotulopex; - 7th December 2025 at 21:43.
    Roger

  15. #15
    Join Date
    May 2013
    Location
    australia
    Posts
    2,705


    Did you find this post helpful? Yes | No

    Default Re: YHDC current sensor - the theory please

    you cannot use a current transformer that way without a burden resistor.
    by voltage sensor do you mean ACS712 or similar ?
    if so that circuit is incorrect, typical use
    Name:  acs712.jpg
Views: 152
Size:  41.4 KB
    Warning I'm not a teacher

  16. #16
    Join Date
    May 2013
    Location
    australia
    Posts
    2,705


    Did you find this post helpful? Yes | No

    Default Re: YHDC current sensor - the theory please

    I can't still figure out what I'm reading.
    the output is intended to be plotted in the freely available easy to use arduino plotter, the average human will have nil chance of interpreting the data with such a small number of samples. if your load current is sinusoidal is should look similar to this

    Name:  peak200.jpg
Views: 148
Size:  107.3 KB
    Warning I'm not a teacher

  17. #17
    Join Date
    May 2013
    Location
    australia
    Posts
    2,705


    Did you find this post helpful? Yes | No

    Default Re: YHDC current sensor - the theory please

    sample data

    Code:
    ADC:1632,peak:608ADC:2447,peak:608
    ADC:3224,peak:608
    ADC:3704,peak:608
    ADC:3722,peak:608
    ADC:3312,peak:3722
    ADC:2528,peak:3722
    ADC:1632,peak:3722
    ADC:880,peak:3722
    ADC:576,peak:3722
    ADC:704,peak:576
    ADC:1248,peak:576
    ADC:2032,peak:576
    ADC:2880,peak:576
    ADC:3520,peak:576
    ADC:3776,peak:576
    ADC:3568,peak:3776
    ADC:2928,peak:3776
    ADC:2032,peak:3776
    ADC:1180,peak:3776
    ADC:644,peak:3776
    ADC:608,peak:3776
    ADC:992,peak:608
    ADC:1656,peak:608
    ADC:2528,peak:608
    ADC:3296,peak:608
    ADC:3714,peak:608
    ADC:3718,peak:608
    ADC:3296,peak:3718
    ADC:2451,peak:3718
    ADC:1551,peak:3718
    ADC:864,peak:3718
    ADC:576,peak:3718
    ADC:736,peak:576
    ADC:1272,peak:576
    ADC:2079,peak:576
    ADC:2928,peak:576
    ADC:3568,peak:576
    ADC:3776,peak:576
    ADC:3552,peak:3776
    ADC:2880,peak:3776
    ADC:1984,peak:3776
    ADC:1138,peak:3776
    ADC:632,peak:3776
    ADC:608,peak:3776
    ADC:1008,peak:608
    ADC:1760,peak:608
    ADC:2608,peak:608
    ADC:3338,peak:608
    ADC:3736,peak:608
    ADC:3696,peak:3736
    ADC:3168,peak:3736
    ADC:2316,peak:3736
    ADC:1423,peak:3736
    ADC:766,peak:3736
    ADC:576,peak:3736
    ADC:792,peak:576
    ADC:1392,peak:576
    ADC:2240,peak:576
    ADC:3056,peak:576
    ADC:3616,peak:576
    ADC:3776,peak:576
    ADC:3462,peak:3776
    ADC:2752,peak:3776
    ADC:1840,peak:3776
    ADC:1031,peak:3776
    ADC:608,peak:3776
    ADC:632,peak:608
    ADC:1088,peak:608
    ADC:1856,peak:608
    ADC:2690,peak:608
    ADC:3424,peak:608
    ADC:3760,peak:608
    ADC:3680,peak:3760
    ADC:3082,peak:3760
    ADC:2240,peak:3760
    ADC:1344,peak:3760
    ADC:736,peak:3760
    ADC:576,peak:3760
    ADC:864,peak:576
    ADC:1472,peak:576
    ADC:2310,peak:576
    ADC:3136,peak:576
    ADC:3680,peak:576
    ADC:3760,peak:576
    ADC:3424,peak:3760
    ADC:2656,peak:3760
    ADC:1760,peak:3760
    ADC:992,peak:3760
    ADC:608,peak:3760
    ADC:646,peak:608
    ADC:1120,peak:608
    ADC:1904,peak:608
    ADC:2752,peak:608
    ADC:3440,peak:608
    ADC:3776,peak:608
    ADC:3648,peak:3776
    ADC:3056,peak:3776
    ADC:2168,peak:3776
    ADC:1295,peak:3776
    ADC:704,peak:3776
    ADC:576,peak:3776
    ADC:880,peak:576
    ADC:1520,peak:576
    ADC:2368,peak:576
    ADC:3168,peak:576
    ADC:3696,peak:576
    ADC:3744,peak:576
    ADC:3376,peak:3744
    ADC:2594,peak:3744
    ADC:1692,peak:3744
    ADC:934,peak:3744
    ADC:608,peak:3744
    ADC:655,peak:608
    ADC:1150,peak:608
    ADC:1934,peak:608
    ADC:2800,peak:608
    ADC:3462,peak:608
    ADC:3760,peak:608
    ADC:3610,peak:3760
    ADC:3008,peak:3760
    ADC:2144,peak:3760
    ADC:1264,peak:3760
    ADC:678,peak:3760
    ADC:576,peak:3760
    ADC:906,peak:576
    ADC:1566,peak:576
    ADC:2416,peak:576
    ADC:3202,peak:576
    ADC:3696,peak:576
    ADC:3738,peak:576
    ADC:3334,peak:3738
    ADC:2544,peak:3738
    ADC:1648,peak:3738
    ADC:899,peak:3738
    ADC:576,peak:3738
    ADC:704,peak:576
    sample wave, note peaks and mid point values
    Name:  RigolDS1.jpg
Views: 145
Size:  156.6 KB
    Warning I'm not a teacher

  18. #18
    Join Date
    Aug 2006
    Location
    SWITZERLAND (french speaking)
    Posts
    952


    Did you find this post helpful? Yes | No

    Default YHDC current sensor - the theory please

    Oh, I get it now, the "plotter".

    I just need to monitor a current level that will trigger a relay.

    I do have ACS712 but the problem is, the current has to pass inside (though) the component meaning I would need to modify the cabling inside an electric board where it is intended to be installed. But I want to avoid this - it has to be like SHELLY energy counters or so.

    I just received a module, an analog AC Current Sensor SEN0211 unsing a YHDC current transformer: DFROBOT. I'll give it a try.
    Last edited by flotulopex; - 8th December 2025 at 09:07.
    Roger

  19. #19
    Join Date
    Aug 2006
    Location
    SWITZERLAND (french speaking)
    Posts
    952


    Did you find this post helpful? Yes | No

    Default YHDC current sensor - the theory please

    you cannot use a current transformer that way without a burden resistor

    Does this mean there is no resistance inside the sensor?

    Name:  YHDC_5-1.png
Views: 146
Size:  130.8 KB
    Roger

  20. #20
    Join Date
    May 2013
    Location
    australia
    Posts
    2,705


    Did you find this post helpful? Yes | No

    Default Re: YHDC current sensor - the theory please

    Does this mean there is no resistance inside the sensor?
    can't tell, the picture is too blurry to read properly but i see no reference to a resistor mentioned it the bits i can read
    post a link to data sheet


    edit
    ps, found this so no resistance inside the sensor

    Name:  Screenshot 2025-12-08 202039.png
Views: 145
Size:  294.3 KB
    Last edited by richard; - 8th December 2025 at 10:25.
    Warning I'm not a teacher

  21. #21


    Did you find this post helpful? Yes | No

    Default Re: YHDC current sensor - the theory please

    if you don't need instantaneous current sensing but can react within 10 or 20 milliseconds..... you can 'filter' the output to DC with the circuit I posted and constantly take a few samples and scale the a/d reading to the amps

  22. #22
    Join Date
    Aug 2006
    Location
    SWITZERLAND (french speaking)
    Posts
    952


    Did you find this post helpful? Yes | No

    Default YHDC current sensor - the theory please

    no resistance inside the sensor
    Again as always: R T Full M
    Roger

  23. #23
    Join Date
    Aug 2006
    Location
    SWITZERLAND (french speaking)
    Posts
    952


    Did you find this post helpful? Yes | No

    Default Re: YHDC current sensor - the theory please

    Quote Originally Posted by amgen View Post
    if you don't need instantaneous current sensing but can react within 10 or 20 milliseconds..... you can 'filter' the output to DC with the circuit I posted and constantly take a few samples and scale the a/d reading to the amps
    I'll go this way, thank you
    Roger

  24. #24
    Join Date
    Aug 2006
    Location
    SWITZERLAND (french speaking)
    Posts
    952


    Did you find this post helpful? Yes | No

    Default YHDC current sensor - the theory please

    ...and from the same supplier:

    Name:  Built-In.jpg
Views: 134
Size:  103.5 KB



    Saint Thomas taps me on my shoulder!

    Name:  Inside V YHDC small.jpg
Views: 137
Size:  49.1 KB


    In the 20A/1V model, there are two resistors and a TVS diode. The first resistor is 1k2 and the second is 1k.

    I also checked a 100A:50mA model and there are no resistors in there, only a TVS diode.
    Last edited by flotulopex; - 9th December 2025 at 18:54.
    Roger

Similar Threads

  1. Current sensor output modification. PIC or opamp or something else?
    By retepsnikrep in forum mel PIC BASIC Pro
    Replies: 9
    Last Post: - 10th December 2020, 06:22
  2. Counter and interrupt theory
    By astouffer in forum mel PIC BASIC Pro
    Replies: 2
    Last Post: - 23rd January 2014, 02:21
  3. Replies: 8
    Last Post: - 5th May 2009, 21:10
  4. current sensor interfacing
    By hell_pk in forum mel PIC BASIC Pro
    Replies: 9
    Last Post: - 29th January 2009, 05:55
  5. PIC based mAh meter/current draw sensor
    By skimask in forum Off Topic
    Replies: 6
    Last Post: - 26th February 2008, 03:10

Members who have read this thread : 14

You do not have permission to view the list of names.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts