A/D Conversion Clock Select bits confussion ..
Results 1 to 30 of 30
    Default Re: A/D Conversion Clock Select bits confussion ..
    if it were possible that the acquisition time could be too long then surely the optimum acquisition time would have to varied logarithmically according to the instantaneous sample voltage . the suggestion is not realistic ,unsubstantiated and unworkable
    Aug 2011
    Agreed.
    Confused...
    Don't be. You have it correct.
    What you're computing is the minimum time it takes for the RC sample/hold network to charge to the input voltage assuming you're making a full-scale voltage change. Depending on the accuracy you're trying to reach that normally takes about 7T-8T. Once it's charged up (or down), you're good to go, but it does no harm in waiting longer (as long as nothing else changes).
    The only thing to watch out for is if you change PIC's be sure to check the specs of the new device. The source resistance of the internal switch and the cap can be different for different families, so that can change the calculation.
    May 2008
    Italy
    Henrik, I am using a rather old pic (18F2620), I still have a couple of hundreds of them. But timing apart your and mine are very similar in the setting of the TAD value and the acquisition time.
    As far as TAD value is concerned I can Select value up to Fosc/64 (minimum delay required for 1 TAD = 1.6 us)
    As far as ACQUISTION TIME is concerned, I have a range selectable from 2 TAD to 20 TAD. (So you have a lower and upper limits)
    I made some experimenting some years ago, using the manual acquisition time, so I could increase/decrease the acquisition time beyond the 2/20 TAD limits. Unfortunatly I was not able to find these data (I have been digging for the whole day without success) but I assure you they were very interesting. The experiment was done taking 100 reading at three specific points of the 10 bits range. First point was fixed to 10 ADC count (low end), second point in the middle at 512 ADC count and the third point at 1012 ADC count (high end). These reading were taken at different acquisition time going from 1 us up to 200 us in steps of 10 us each.
    Once, all the data were collected ( they have been collected via RS232 connection and loaded directly into an Excel sheet), the statistic applied were : Average/Standard deviation/standard error.
    Looking at the standard error, I noticed an increase in the two extreme regions when the acquisition time was too low or higher than the 2/20 TADs region , no significant variation of standard error were observed in the middle range.
    I will continue to search these files (I am sure I still have them somewhere) and If I found them I will post them here in this thread.
    But everybody, with some time to spare, can repeat the experiment on his own.
    Cheers.
    Al
    OK, I did the test.
    For this I was using a 18F25K20 running at 64MHz and 3.3V. Vref set to VDD/VSS and measured at 2.999V.
    Actual voltages measured with a FLUKE189
    The test program cycles thru all the available clock selections and all the available acquisition times (49 combinations). For each selection it takes 8 readings on AN0. Between each reading it makes a dummy conversion of another (floating) channel. After 8 readings it calculates the averages and presents the result.
    The test was conducted at 3 different input voltages (25mV, 1.65V, 3.285V) with 3 different source impedences (1k, 10k, 39k). For the 18F25K20 10k is the max recommended source impedence.
    Here's the code if anyone wants to repeat the test.
    Please note the ADC clock and acquisition time may be different on other devices, this matches the 25K20 that I used:
    '*  Name    : ADC Test.PBP                                      *
    '*  Author  : Henrik Olsson                                     *
    '*  Notice  : Copyright (c) 2015 Henrik Olsson                  *
    '*  Date    : 2015-07-23                                        *
    '*  Notes   : Test program for verifying ADC clock selection    *
    '*          : and acquisition times.                            *
    '*          : For 18F25K20.                                     *
    DEFINE OSC 64
    DEFINE LOADER_USED 1                        ' We're using a bootloader.
    DEFINE HSER_RCSTA 90h                       ' Enable serial port & continuous receive
    DEFINE HSER_TXSTA 24h                       ' Enable transmit, BRGH = 1
    DEFINE HSER_CLROERR 1                       ' Clear overflow automatically
    DEFINE HSER_SPBRG 138                       ' 115200 Baud @ 64MHz, -0,08%
    SPBRGH = 0
    BAUDCON.3 = 1                               ' Enable 16 bit baudrate generator
    ADCON0 = %00000001                          ' Enable the ADC, select AN0
    ADCON1 = %00000000                          ' Vref is Vdd/Vss respectively
    ADCON2 = %10001000                          ' Right justified result, 2TAD, FOosc/2
    TRISA.0 = 1                                 ' RA0/AN0 is input
    ANSEL.0 = 1                                 ' Digital buffer disabled, analog enabled
    Samples VAR BYTE
    ACQT VAR BYTE
    ADCS VAR BYTE
    RESULT VAR WORD
    Accumulator VAR WORD
    GODONE VAR ADCON0.1
    PAUSE 1000
    HSEROUT["Start",10,13]
    For ACQT = 1 to 7                           ' We have 7 different TAD settings ranging from 2TAD to 20TAD
        For ADCS = 0 to 6                       ' We hace 7 different conversion clock selections
            ADCON2 = 128 + (ACQT * 8) + ADCS    ' "Build the ADCON2 word by combining the two settings.
            PAUSE 25
            Accumulator = 0
            For samples = 0 to 7                ' Take 8 samples
                ' First make a dummy conversion of a channel we're not really interested in
                ADCON0.2 = 1
                GODONE = 1
                WHILE GODONE : WEND
                ' Then switch to AN0 and make a conversion.
                ADCON0.2 = 0
                GODONE = 1
                WHILE GODONE : WEND
                ' Get the result and add it to the accumulator
                Result.HighByte=ADRESH
                Result.LOWBYTE=ADRESL
                Accumulator = Accumulator + Result
            NEXT
            ' Divide accumulated result by 8 to get the average of our 8 readings.
            Result = Accumulator >> 3
            ' These selections matches the 18F25K20
            Select CASE ADCS
                CASE 0
                    HSEROUT["FOSC/2     "]
                CASE 1
                    HSEROUT["FOSC/8     "]
                CASE 2
                    HSEROUT["FOSC/32    "]
                CASE 3
                    HSEROUT["FRC        "]
                CASE 4
                    HSEROUT["FOSC/4     "]
                CASE 5
                    HSEROUT["FOSC/16    "]
                CASE 6
                    HSEROUT["FOSC/64    "]
            END Select
            SELECT CASE ACQT
                CASE 1
                    HSEROUT["2 TAD    "]
                CASE 2
                    HSEROUT["4 TAD    "]
                CASE 3
                    HSEROUT["6 TAD    "]
                CASE 4
                    HSEROUT["8 TAD    "]
                CASE 5
                    HSEROUT["12 TAD   "]
                CASE 6
                    HSEROUT["16 TAD   "]
                CASE 7
                    HSEROUT["20 TAD   "]
            END SELECT
            ' Report the result.
            HSEROUT["  Result: ", #RESULT, 13]
        NEXT
    NEXT
    PAUSE 100
    And here are the results:
    VRef is VDD/VSS measured to 3.299V
    1k resistor in series with input
    Input voltage 25.7mV
    FOSC/2     2 TAD      Result: 8
    FOSC/8     2 TAD      Result: 8
    FOSC/32    2 TAD      Result: 7
    FRC        2 TAD      Result: 7
    FOSC/4     2 TAD      Result: 8
    FOSC/16    2 TAD      Result: 7
    FOSC/64    2 TAD      Result: 7
    FOSC/2     4 TAD      Result: 9
    FOSC/8     4 TAD      Result: 7
    FOSC/32    4 TAD      Result: 7
    FRC        4 TAD      Result: 7
    FOSC/4     4 TAD      Result: 8
    FOSC/16    4 TAD      Result: 7
    FOSC/64    4 TAD      Result: 7
    FOSC/2     6 TAD      Result: 8
    FOSC/8     6 TAD      Result: 7
    FOSC/32    6 TAD      Result: 7
    FRC        6 TAD      Result: 7
    FOSC/4     6 TAD      Result: 7
    FOSC/16    6 TAD      Result: 7
    FOSC/64    6 TAD      Result: 7
    FOSC/2     8 TAD      Result: 8
    FOSC/8     8 TAD      Result: 7
    FOSC/32    8 TAD      Result: 6
    FRC        8 TAD      Result: 7
    FOSC/4     8 TAD      Result: 7
    FOSC/16    8 TAD      Result: 7
    FOSC/64    8 TAD      Result: 7
    FOSC/2     12 TAD     Result: 8
    FOSC/8     12 TAD     Result: 8
    FOSC/32    12 TAD     Result: 7
    FRC        12 TAD     Result: 7
    FOSC/4     12 TAD     Result: 7
    FOSC/16    12 TAD     Result: 7
    FOSC/64    12 TAD     Result: 7
    FOSC/2     16 TAD     Result: 8
    FOSC/8     16 TAD     Result: 7
    FOSC/32    16 TAD     Result: 7
    FRC        16 TAD     Result: 7
    FOSC/4     16 TAD     Result: 7
    FOSC/16    16 TAD     Result: 7
    FOSC/64    16 TAD     Result: 7
    FOSC/2     20 TAD     Result: 8
    FOSC/8     20 TAD     Result: 7
    FOSC/32    20 TAD     Result: 7
    FRC        20 TAD     Result: 7
    FOSC/4     20 TAD     Result: 7
    FOSC/16    20 TAD     Result: 7
    FOSC/64    20 TAD     Result: 7
    Input Voltage: 1.650V
    FOSC/2     2 TAD      Result: 497
    FOSC/8     2 TAD      Result: 509
    FOSC/32    2 TAD      Result: 511
    FRC        2 TAD      Result: 511
    FOSC/4     2 TAD      Result: 508
    FOSC/16    2 TAD      Result: 511
    FOSC/64    2 TAD      Result: 511
    FOSC/2     4 TAD      Result: 504
    FOSC/8     4 TAD      Result: 511
    FOSC/32    4 TAD      Result: 511
    FRC        4 TAD      Result: 511
    FOSC/4     4 TAD      Result: 512
    FOSC/16    4 TAD      Result: 511
    FOSC/64    4 TAD      Result: 511
    FOSC/2     6 TAD      Result: 507
    FOSC/8     6 TAD      Result: 511
    FOSC/32    6 TAD      Result: 511
    FRC        6 TAD      Result: 511
    FOSC/4     6 TAD      Result: 512
    FOSC/16    6 TAD      Result: 511
    FOSC/64    6 TAD      Result: 511
    FOSC/2     8 TAD      Result: 509
    FOSC/8     8 TAD      Result: 511
    FOSC/32    8 TAD      Result: 511
    FRC        8 TAD      Result: 511
    FOSC/4     8 TAD      Result: 512
    FOSC/16    8 TAD      Result: 511
    FOSC/64    8 TAD      Result: 511
    FOSC/2     12 TAD     Result: 511
    FOSC/8     12 TAD     Result: 511
    FOSC/32    12 TAD     Result: 511
    FRC        12 TAD     Result: 512
    FOSC/4     12 TAD     Result: 512
    FOSC/16    12 TAD     Result: 511
    FOSC/64    12 TAD     Result: 511
    FOSC/2     16 TAD     Result: 511
    FOSC/8     16 TAD     Result: 511
    FOSC/32    16 TAD     Result: 511
    FRC        16 TAD     Result: 511
    FOSC/4     16 TAD     Result: 512
    FOSC/16    16 TAD     Result: 511
    FOSC/64    16 TAD     Result: 511
    FOSC/2     20 TAD     Result: 511
    FOSC/8     20 TAD     Result: 511
    FOSC/32    20 TAD     Result: 511
    FRC        20 TAD     Result: 511
    FOSC/4     20 TAD     Result: 512
    FOSC/16    20 TAD     Result: 512
    FOSC/64    20 TAD     Result: 511
    Input Voltage: 3.286V
    FOSC/2     2 TAD      Result: 511
    FOSC/8     2 TAD      Result: 1013
    FOSC/32    2 TAD      Result: 1019
    FRC        2 TAD      Result: 1019
    FOSC/4     2 TAD      Result: 995
    FOSC/16    2 TAD      Result: 1018
    FOSC/64    2 TAD      Result: 1019
    FOSC/2     4 TAD      Result: 511
    FOSC/8     4 TAD      Result: 1019
    FOSC/32    4 TAD      Result: 1019
    FRC        4 TAD      Result: 1020
    FOSC/4     4 TAD      Result: 1011
    FOSC/16    4 TAD      Result: 1020
    FOSC/64    4 TAD      Result: 1019
    FOSC/2     6 TAD      Result: 1006
    FOSC/8     6 TAD      Result: 1019
    FOSC/32    6 TAD      Result: 1019
    FRC        6 TAD      Result: 1020
    FOSC/4     6 TAD      Result: 1016
    FOSC/16    6 TAD      Result: 1019
    FOSC/64    6 TAD      Result: 1019
    FOSC/2     8 TAD      Result: 1014
    FOSC/8     8 TAD      Result: 1020
    FOSC/32    8 TAD      Result: 1019
    FRC        8 TAD      Result: 1019
    FOSC/4     8 TAD      Result: 1018
    FOSC/16    8 TAD      Result: 1019
    FOSC/64    8 TAD      Result: 1019
    FOSC/2     12 TAD     Result: 1017
    FOSC/8     12 TAD     Result: 1019
    FOSC/32    12 TAD     Result: 1019
    FRC        12 TAD     Result: 1019
    FOSC/4     12 TAD     Result: 1020
    FOSC/16    12 TAD     Result: 1019
    FOSC/64    12 TAD     Result: 1019
    FOSC/2     16 TAD     Result: 1019
    FOSC/8     16 TAD     Result: 1019
    FOSC/32    16 TAD     Result: 1019
    FRC        16 TAD     Result: 1019
    FOSC/4     16 TAD     Result: 1020
    FOSC/16    16 TAD     Result: 1019
    FOSC/64    16 TAD     Result: 1019
    FOSC/2     20 TAD     Result: 1020
    FOSC/8     20 TAD     Result: 1020
    FOSC/32    20 TAD     Result: 1019
    FRC        20 TAD     Result: 1019
    FOSC/4     20 TAD     Result: 1020
    FOSC/16    20 TAD     Result: 1020
    FOSC/64    20 TAD     Result: 1019
    10k resistor in series with input
    FOSC/2     2 TAD      Result: 9
    FRC        2 TAD      Result: 7
    FOSC/2     4 TAD      Result: 8
    FRC        4 TAD      Result: 7
    FRC        6 TAD      Result: 7
    FOSC/32    8 TAD      Result: 7
    FRC        8 TAD      Result: 7
    FOSC/8     12 TAD     Result: 7
    FOSC/8     16 TAD     Result: 8
    FOSC/4     16 TAD     Result: 8
    Input voltage 1.650V
    FOSC/2     2 TAD      Result: 445
    FOSC/8     2 TAD      Result: 471
    FOSC/32    2 TAD      Result: 508
    FOSC/4     2 TAD      Result: 448
    FOSC/16    2 TAD      Result: 494
    FOSC/2     4 TAD      Result: 457
    FOSC/8     4 TAD      Result: 493
    FOSC/4     4 TAD      Result: 470
    FOSC/16    4 TAD      Result: 507
    FOSC/2     6 TAD      Result: 461
    FOSC/8     6 TAD      Result: 503
    FOSC/4     6 TAD      Result: 485
    FOSC/16    6 TAD      Result: 510
    FOSC/2     8 TAD      Result: 472
    FOSC/8     8 TAD      Result: 507
    FOSC/4     8 TAD      Result: 494
    FOSC/2     12 TAD     Result: 478
    FOSC/8     12 TAD     Result: 510
    FRC        12 TAD     Result: 511
    FOSC/4     12 TAD     Result: 510
    FOSC/2     16 TAD     Result: 493
    FOSC/2     20 TAD     Result: 503
    FOSC/16    20 TAD     Result: 511
    Input voltage 3.286V
    FOSC/8     2 TAD      Result: 929
    FOSC/32    2 TAD      Result: 1012
    FOSC/4     2 TAD      Result: 880
    FOSC/16    2 TAD      Result: 981
    FOSC/8     4 TAD      Result: 980
    FOSC/32    4 TAD      Result: 1018
    FRC        4 TAD      Result: 1019
    FOSC/4     4 TAD      Result: 926
    FOSC/16    4 TAD      Result: 1011
    FOSC/2     6 TAD      Result: 511
    FOSC/8     6 TAD      Result: 1001
    FOSC/4     6 TAD      Result: 959
    FOSC/16    6 TAD      Result: 1017
    FOSC/2     8 TAD      Result: 511
    FOSC/8     8 TAD      Result: 1010
    FOSC/4     8 TAD      Result: 979
    FOSC/8     12 TAD     Result: 1017
    FOSC/32    12 TAD     Result: 1020
    FRC        12 TAD     Result: 1020
    FOSC/4     12 TAD     Result: 1000
    FOSC/2     16 TAD     Result: 923
    FOSC/4     16 TAD     Result: 1010
    FOSC/2     20 TAD     Result: 990
    FOSC/8     20 TAD     Result: 1019
    FRC        20 TAD     Result: 1020
    FOSC/4     20 TAD     Result: 1015
    FOSC/16    20 TAD     Result: 1019
    39k resistor in series with input
    Input voltage: 25.7mV
    FOSC/2     2 TAD      Result: 11
    FOSC/8     2 TAD      Result: 7
    FRC        2 TAD      Result: 7
    FRC        4 TAD      Result: 7
    FOSC/4     4 TAD      Result: 7
    FOSC/8     6 TAD      Result: 8
    FRC        6 TAD      Result: 7
    FOSC/4     6 TAD      Result: 8
    FRC        8 TAD      Result: 7
    FOSC/4     8 TAD      Result: 8
    FOSC/2     12 TAD     Result: 9
    FOSC/16    12 TAD     Result: 8
    Input voltage: 1.650V
    FOSC/2     2 TAD      Result: 406
    FOSC/8     2 TAD      Result: 420
    FOSC/32    2 TAD      Result: 470
    FRC        2 TAD      Result: 507
    FOSC/4     2 TAD      Result: 407
    FOSC/16    2 TAD      Result: 441
    FOSC/64    2 TAD      Result: 496
    FOSC/2     4 TAD      Result: 408
    FOSC/8     4 TAD      Result: 439
    FOSC/32    4 TAD      Result: 495
    FOSC/4     4 TAD      Result: 418
    FOSC/16    4 TAD      Result: 469
    FOSC/64    4 TAD      Result: 509
    FOSC/2     6 TAD      Result: 415
    FOSC/8     6 TAD      Result: 457
    FOSC/32    6 TAD      Result: 505
    FOSC/4     6 TAD      Result: 428
    FOSC/16    6 TAD      Result: 485
    FOSC/2     8 TAD      Result: 418
    FOSC/8     8 TAD      Result: 469
    FOSC/32    8 TAD      Result: 509
    FRC        8 TAD      Result: 512
    FOSC/4     8 TAD      Result: 442
    FOSC/16    8 TAD      Result: 495
    FOSC/2     12 TAD     Result: 427
    FOSC/8     12 TAD     Result: 486
    FOSC/4     12 TAD     Result: 456
    FOSC/16    12 TAD     Result: 506
    FOSC/2     16 TAD     Result: 450
    FOSC/8     16 TAD     Result: 496
    FRC        16 TAD     Result: 512
    FOSC/4     16 TAD     Result: 469
    FOSC/16    16 TAD     Result: 509
    FOSC/2     20 TAD     Result: 453
    FOSC/8     20 TAD     Result: 502
    FOSC/4     20 TAD     Result: 478
    FOSC/16    20 TAD     Result: 510
    Input voltage: 3.286V
    FOSC/2     2 TAD      Result: 768
    FOSC/8     2 TAD      Result: 826
    FOSC/32    2 TAD      Result: 931
    FRC        2 TAD      Result: 1010
    FOSC/4     2 TAD      Result: 801
    FOSC/16    2 TAD      Result: 873
    FOSC/64    2 TAD      Result: 986
    FOSC/8     4 TAD      Result: 867
    FOSC/32    4 TAD      Result: 984
    FOSC/4     4 TAD      Result: 824
    FOSC/16    4 TAD      Result: 929
    FOSC/64    4 TAD      Result: 1014
    FOSC/8     6 TAD      Result: 904
    FOSC/32    6 TAD      Result: 1006
    FRC        6 TAD      Result: 1019
    FOSC/4     6 TAD      Result: 847
    FOSC/16    6 TAD      Result: 963
    FOSC/8     8 TAD      Result: 930
    FOSC/32    8 TAD      Result: 1014
    FOSC/4     8 TAD      Result: 874
    FOSC/16    8 TAD      Result: 985
    FOSC/8     12 TAD     Result: 963
    FOSC/4     12 TAD     Result: 901
    FOSC/16    12 TAD     Result: 1006
    FOSC/2     16 TAD     Result: 847
    FOSC/8     16 TAD     Result: 985
    FOSC/4     16 TAD     Result: 927
    FOSC/16    16 TAD     Result: 1015
    FOSC/2     20 TAD     Result: 847
    FOSC/8     20 TAD     Result: 999
    FOSC/4     20 TAD     Result: 950
    FOSC/16    20 TAD     Result: 1017
    I haven't analyzed any of it yet and I don't have any more time just now but I wanted to post the results. If anyone wants to graph the results in Excel or whatever to better see what's going on, please feel free to do so.
    Aug 2011
    You certainly coverted all the bases! Good job.
    Instead of bothering to graph all the data and try and make sense of it, Let's start with this:
    The 25K20 has a TAD spec of 0.7us min.
    At 64MHz, that means all ADCS settings except for FOSC/64 and FRC violate minimum times (Table 19-1).
    Using the FOSC/64 setting gives a TAD of 1us
    Computing Tc from equation 19-1 for each of the three source resistances gives:
    1K = 0.27us
    10K = 1.2us
    39K = 4.2us
    Computing TACQ = Tamp + Tc + Tcoff, given Tamp = 5us and Tcoff = 0 (25degC) produces:
    1K = 5.27us
    10K = 6.2us
    39K = 9.2us
    So, since TAD = 1us, TACQ must be a min of ~6-9 TAD for the three different resistances.
    Removing all of the measurements that don't fit the above you get:
    1k resistor in series with input (TACQ=5.27us)
    FRC        6 TAD      Result: 7
    FRC        8 TAD      Result: 7
    10k resistor in series with input  (TACQ=6.2us)
    FRC        6 TAD      Result: 7
    FRC        8 TAD      Result: 7
    39k resistor in series with input  (TACQ=9.2us)
    FRC        6 TAD      Result: 7
    FRC        8 TAD      Result: 7
    Pretty consistent. It shows that waiting longer than the minimum doesn't get you anything, but it also doesn't change anything either.
    The interesting thing is as you look through the raw data you can see the effect of not using the proper TAD setting for the clock freq you're using, or not waiting/setting TACQ to at least the minimum time.
  1. Replies: 2
    Last Post: - 23rd April 2013, 17:34
  2. DT_INTS-14 /interrupts enable bits / flag bits
    By bogdan in forum mel PIC BASIC Pro
    Last Post: - 16th May 2009, 19:42
  3. external clock / internal clock
    By grounded in forum General
    Last Post: - 31st May 2008, 18:44
  4. IF or SELECT
    By RYTECH in forum mel PIC BASIC Pro
    Last Post: - 31st December 2005, 19:31
  5. Need clever way to convert 10 bits to 8 bits
    By MikeTamu in forum mel PIC BASIC Pro
    Last Post: - 2nd September 2005, 16:13