Need help with understanding PID control
Results 1 to 12 of 12
    Nov 2009
    London
    Default Need help with understanding PID control
    I have to make a PID temperature control. I do not want to use any existing inc files though they have helped a lot in understanding. I am starting from basics and would like some help in understanding a few concepts. I am starting with only proportional control for now and will develop the whole code as I go along and will post the whole working code at the end. So, here I go:
    I have a 12 bit adc with LM35 connected to it. I have a 16f877a which runs the show.
    My questions are:
    1) When the error is -ve or zero (i.e. current value is greater than or equal to the set point )then should proportional drive become zero? (i.e. if error.15=1 then prop_drive=0)
    2) Can Kp be a positive integer between 1 to 100 or is it better to have it as 1-10 with 2 decimal digit. i.e 1.12/2.34/5.88 ....etc?
    3) How does a 0-255 duty cycle relates to value in few hundreds or thousands of proportional drive? For example, if MAX set point is 55 degrees or 416 ADC value and current reading is 200, error is 216, lets say kp is 5 then proportional drive will be 216 x 5 which is far higher than MAX duty cycle of 255. So how do I relate the drive to a number between 0-255?
    These are the initial questions I am looking for answers for and will have more as I go along. Thanks
    Default Re: Need help with understanding PID control
    When the error is zero the proportional term will be zero. When the error is negative the proportional output should be negative (even if you clamp the final output to positive values).
    Just a matter of taste. Since PBP doesn't support floating point numbers natively you're going to end up with integers anyway. The more resolution you have the better control you'll be able to get.
    That's up to you really. If the gain actually IS 5 then the output will gat saturated. But if the gain is represented as you outline above, where 5 might mean 0.5 or 0.05 then the P-term would be 108 or 10.
    If large changes in setpoint is to be expected while the regulator is working then I'd suggest you implement some sort of ramp with a slope that the system is capable of following otherwise you'll get into situations as above where there's a HUGE error resulting in a saturated output and integrator windup (which you need to cater for). So, if you (the user) change the setpoint from 100 to 200 then allow the system to internally ramp the setpoint for the regulator up from 100 to 200 along a slope that whatever it is you're regulating can actually follow.
    Nov 2009
    London
    Thanks Henrik. I have got one more question for you, for now:
    pid_Kp = $0700                     'Set Kp to 7.0
    pid_Ki = $0080                     'Set Ki to 0.5
    pid_Kd = $0225                     'Set Kd to 2.14
    In your code above, you take $0225 to 2.14, $0080 to 0.5, how is that? I do not see calculations for converting numbers to decimal digits, as you are multiplying them as it is to the error variable. Please explain me how this is working and I will also be interested in knowing what is the maximum number I can assign to the gain this way, I will clamp it later as I intend to use pot for setting these. Cheers
    It's because the calculations are using the */ operator: 100 */ $0225 = 214
    Since the gain variables (kp, ki, kd) are Words the max gain would obviosuly be $FFFF which is equal to an actual gain of ~255. Care needs to be taken not to overflow the output when large gains are used in system where the error cn be large.
    Nov 2009
    London
    Thanks Henrik. So, is there any way I can tell what is the actual gain setting ( like 2.14 or 3.5 etc) before I multiply with 10 or 100. For example just by looking at lets say for example $0324?
    I tried the following code, but my duty stays at 255 and is not coming down after overshoot.
    'PROPORTIONAL VARIABLES
    Error_P Var Word
    Kp Var Word
    Kp=$0900
    Gosub Get_Sensor_Value ' Get value from sensor
    ' ----- PROPORTIONAL CONTROL----------
    Error_P=Set_Point-Sensor
    Drive_p=(ABS Error_P) */ Kp
    If Error_P.15 then Drive_P=-Drive_P
    Drive_T=Drive_T+Drive_P '(I used DriveT=Drive_T+... to keep some level of drive)
    Duty=Drive_T
    Gosub Duty_Mosfet
    Pause 250
    Goto Main
    Duty_Mosfet:
    If Duty>255 then Duty=255
    If Duty.15=1 then Duty=0
    HPWM 1,Duty,500
    hex 324 = dec 804 , 804/256 = 3.14
    Richard covered the gain calculations, not much to add to that.
    Your problem is most likely the line
    Drive_T will accumulate to very large numbers and you don't show what type variable it is. If it's BYTE then you'll be in even more trouble because it won't work properly adding Drive_P when that value is negative. For that to work both variables need to be the same size - which they might be, I don't know since you don't show the code. If you insist on keeping that line you should probably consider clamping Drive_T too so that it won't go higher than 255 in this case.
    With a gain of 9 ($0900) the output will be saturated whenver the error is 29 or more (because 29*9=261). To get more resolution I'd probably skip using HPWM and set the CCP module up manually, that way you can 10bit PWM resolution instead of 8.
    with a little bit of experimenting you should be able to find the approximate amount of drive needed to maintain your chosen temperature . then use the p_error * kp _value to vary your pwm drive about this point. its best to start with a small kp and increase it till the temp oscillates about your set point . if the load conditions vary substancially however or you wish to vary the set point over a large range you may need use a full pid filter .
    ps look up pid in Wikipedia for a good insight
    Nov 2009
    London
    Ok, I am actually starting to understand it better now, thanks to all.
    I would like to ask, if I use pot to set this gain, the maximum decimal value I will get is 1024 i.e. $0400 (1024/256) which is 4 in terms of Kp. How do I increase Kp if I want to? (If I multiply Kp by 2 or 3 or 4 etc then I start to skip few 2nd decimal digits (pic attached). Any way around it?Name:  Capture.PNG
    Well, you could introduce some oversampling and increase the effective resolution from 10 to say 12 bits. Ie take 40 samples, add them up and divide the result by 10, you now have a 12bit value instead of a 10bit one. Or, you could use two pots, one for coarse and one for fine adjustment.
    However, I wouldn't worry too much about dropping a digit after the decimal point. Just do what you we're going to and multiply your ADC value with whatever you need to get into the range that you want, it'll work fine.
    Nov 2009
    London
    Thanks a lot. I now will start with the prop control and add integral and then post the code to discuss any issues.
    Jan 2011
    Sydney, Australia
    If you need to increase the gain greater than 1024 (1024/256 = 4) without losing resolution then simply add 1024 to the ADC pot value (range 1024-2048).
    If you still need more gain then add 2048 to the ADC pot value (range 2048 -3072).
    I do agree with Henrik though, don't worry too much about dropping a digit after the decimal point.
    Perhaps use the multiplication method to quickly get you into the ball park and then use the addition method to fine tune the control if required.
    This is the method I used to tune my motor speed controller PID loop.
    Cheers
    Barry
    VK2XBP
  1. PID help
    Last Post: - 4th November 2011, 07:32
  2. Replies: 0
    Last Post: - 27th March 2011, 21:10
  3. Re: PID control + radiant heating
    By Steve_88 in forum Off Topic
    Last Post: - 18th January 2011, 14:11
  4. Pid
    By colarsson in forum mel PIC BASIC Pro
    Last Post: - 2nd November 2005, 11:18
  5. PID control with Picbasicpro
    By swordman in forum mel PIC BASIC Pro
    Last Post: - 6th August 2004, 15:37