12V PLC sensor to 3.3V input


Closed Thread
Results 1 to 4 of 4

Hybrid View

  1. #1
    Join Date
    Mar 2006
    Location
    China
    Posts
    266


    Did you find this post helpful? Yes | No

    Default Re: 12V PLC sensor to 3.3V input

    Tack för dina förslag!

    I had to mix a litle from both your ideas. The sensor seems to have a really weak internal pullup to 12V so as soon as I connect the resistor divider the voltage drops alot. And without the divider the PIC gets 12V on the pin.

    So I ended up introducing a new pullup resistor to 12V to the output .. and then a resistor divider from that. Weird but working

  2. #2
    Join Date
    Aug 2012
    Posts
    2


    Did you find this post helpful? Yes | No

    Default Re: 12V PLC sensor to 3.3V input

    Is this a 2-wire or 3-wire proximity. As for 3-wire nothing wrong to use resistor devider but for 2-wire, the sensor will not get enough voltage across it or minimum current to function properly.