    Default Inductive load surge problem

    If your final load is inductive, then the best solution is a zero crossing turn-on and a MOV protected zero crossing turn-off is the easiest solution. See: http://www.power-io.com/new/motorstarters.htm
    as an example of this.

  2. #2
    Join Date
    Feb 2004
    Location
    Germany
    Posts
    762


    Did you find this post helpful? Yes | No

    Default

    Mike,

    thanks for the link,
    the price is as high as the heatsink is large
    ;-)
    Last edited by NavMicroSystems; - 11th April 2005 at 00:21.
    regards

    Ralph

    _______________________________________________
    There are only 10 types of people:
    Those who understand binary, and those who don't ...
    _______________________________________________



  3. #3
    Join Date
    Jul 2003
    Posts
    2,358


    Did you find this post helpful? Yes | No

    Default

    Sorry Ralph I wasn't continuing to read this thread as I'd assumed it had already been adequately answered some days ago...

    Yes, zero cross is the way to go with inductive loads, plus VDR's (capable of absorbing any transients) across the switching element.

    Ensure inductive surges will not penetrate your PSU and it is clean. You've sprinked 100nF Capacitors around your power rails like confetti.

    Basic filtering on any other input pins (you'll be surprised what a 10K Resistor and a 100nF Capacitor will stop!).

    Site the PIC well away from your switching elements or ensure it is screened and if nescessary has a large ground plane all around and underneath it.

    I've not experienced the PIC problems that a lot of folks seem to have, perhaps it's because I build-in all the above recommendations into my PIC designs from the very beginning. It is important to identify what kind of interference is causing your problem... without knowing that you're stabbing in the dark as to a solution. It's overly simplistic saying it's "an inductive load switching". well what's it doing? Is the transient going down the power lines and affecting your PSU? Is it being induced into PCB tracks and coming down other input pins (or being induced locally into the PSU)? Or is it a localised EMP screwing the chip directly. You MUST first identify the root cause before applying a solution otherwise you will just end up wasting hours of your life.

  4. #4
    Join Date
    Feb 2004
    Location
    Germany
    Posts
    762


    Did you find this post helpful? Yes | No

    Default

    Thanks Melanie!
    regards

    Ralph

    _______________________________________________
    There are only 10 types of people:
    Those who understand binary, and those who don't ...
    _______________________________________________



  5. #5


    Did you find this post helpful? Yes | No

    Default

    First, thanks for all the help here.

    Unfortunately I was not aware of this problem when switching AC relays. We can rule out the load on the relay because we can get the circuit to reset on the bench with no load on it. This makes me think that there is a nasty little spike travelling down through the ground back to my board. If I insert an MOV at the relay the problem seems to disapear. However this I consider a not so easy to implement solution since there about 400 of these products out in the field right now that need to be corrected.

    As for driving the relays I use a small signal relay that switches the 24VAC to the larger relay. The small relay is driven from a transistor connected between it and ground. I then have the base connected to the PIC via a 10k resistor.

    As for solid state relay, way too expensive and way to much real estate. Would be nice but not doable.
    Last edited by CocaColaKid; - 13th April 2005 at 18:42.

  6. #6
    Join Date
    Oct 2004
    Location
    Italy
    Posts
    695


    Did you find this post helpful? Yes | No

    Default

    Post the model number and brand of the large relay.
    (URL where we can see the large relay + datasheet).

    Luciano

  7. #7


    Did you find this post helpful? Yes | No

    Default

    I was just looking at some relays and noticed that Panasonic has some SSR that have a zero-cross built-in. This would eliminate the need to use my small signal relay + transistor to fire the larger relays while providing a zero-cross circuit for a cheaper price.

Similar Threads

  1. Need Help
    By PVBiljon in forum mel PIC BASIC Pro
    Replies: 4
    Last Post: - 29th May 2009, 17:04
  2. Replies: 24
    Last Post: - 7th November 2008, 04:41
  3. DC - AC Solid State Relay
    By shahidali55 in forum General
    Replies: 6
    Last Post: - 10th November 2007, 16:01
  4. Serial Relays
    By tazntex in forum General
    Replies: 3
    Last Post: - 17th May 2007, 17:42
  5. Replies: 22
    Last Post: - 9th April 2007, 15:25

Members who have read this thread : 0

You do not have permission to view the list of names.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts