We keep getting whacked by these huge spikes when we switch off the loads.

Originally Posted by
cupajoe
Are you sure that the noise isn't coming from the coil of the relay? Can you hook a relay up to your pic without a load and fire it and scope the noise?
I have had a simmilar situation,
with no load I could switch all relays without seeing any spike,
but with (inductive) load on the large relais I had huge spikes about 1 or 2 times out of 10.
The spikes were definitely comming from the relays contacts when opening.
Since the "power-side" of the project was an existing installation, replacing the relays was no option.
This is why I went for the "ZeroCrossing" solution.
@CocaColaKid,
However you should doublecheck you have done everything to suppress noise comming from the coils.
Make sure you have proper grounding and no Ground loops.
Use a separat PSU to drive the small relays.
@Melanie
Isn't this one of the areas you are experienced in?
Last edited by NavMicroSystems; - 6th April 2005 at 15:54.
regards
Ralph