Time Proportional Control Example?
Results 1 to 6 of 6
    Default Re: Time Proportional Control Example?
    Hello Curtis
    Welcome to the forum.
    Your problem can be broken down into 2 parts
    1 - caluclate the value of output power via your PI routine
    2 - convert this power to a time value
    From your question, I guess, you have no issues with point 1
    Assume you have power going from 0 to 100% corresponding from full off to full on. This can be converted to time thus
    If the cycle time Tcyc you specified for your controller is - let us say - 10 seconds
    On time will be
    Ton = (Tcyc * Power) / 100
    With this, you will get a Ton ranging from 0 - 10 seconds
    Now, to control the duty cycle of your heater using this value, you can do this
    Tvar var word
    Tvar is a variable that runs from 0 to 10 seconds.
    Tvar = Tvar + 1
    if Tvar >= 10 then Tvar = 0 ' roll over
    if Tvar < Ton then
    gosub HeaterOn
    gosub HeaterOff
    I hope this will help you
    Oh, I forgot to add that you need to have the code above run at a fixed 1 second rate to get correct results
    Very good! You made it look so simple. I'll be sure to post the code once it is all worked out.
    Curtis
    Aug 2010
    Maryland, USA
    Yup, as I said, my lack of understanding. Thank you for the links Curtis. It may just be time for me to start playing with PID. Good luck with your project