PID Problem
Results 1 to 10 of 10
Thread: PID Problem
    Default Re: PID Problem
    Still not quite there....
    Below is the code with the If pid_Out.15 Then pid_Out = 0 included.
    pid_Out = ABS pid_Out              'Convert from two's comp. to absolute
    No, this completely defeats the purpose. You can't first say ABS and THEN check if it's negative - it'll NEVER be negative AFTER you've converted it to ABSsoulte. Simply remove the pid_Out = ABS pid_Out all together.
    And you're still trying to squeeze the result of a LONG-LONG subtraction into a WORD sized variable and I'm not sure if or how that is going to work.
    Changed the LONGS to WORDS and removed the ABS line. Its still the same. I just don't understand how it is going to change the DUTY4 number to what is really needed. I have to be missing something.
    define CODE_SIZE 32
    define osc 20
    Include "modedefs.bas"	' Mode definitions for Serout
    INCLUDE "incPID.pbp"                 'Include the PID routine.
    ADValue VAR WORD                     '<---This is your variable.
    SetPoint VAR WORD                    '<---This is your variable.
    OnOff1         var     PortE.1             'Input Signal from GPS to activate/deactivate row
    OnOff2         var     PortE.0             'Input Signal from GPS to activate/deactivate row
    OnOff3         var     PortA.5             'Input Signal from GPS to activate/deactivate row
    OnOff4         var     PortB.5             'Input Signal from GPS to activate/deactivate row
    Switch1        var     PortD.0             ''Output to 4066; activates Speed1
    Switch2        var     PortE.2             ''Output to 4066; activates Speed2
    Switch3        var     PortC.0             ''Output to 4066; activates Speed3
    Switch4        var     PortC.3             ''Output to 4066; activates Speed4
    MotorSpeed     var     PortC.1             'Input from 4066
    Population     var     PortC.2             'Input from GPS
    Enable1        var     PortD.1             ''Output Turns on Motor1 driver
    Enable2        var     PortD.2             ''Output Turns on Motor2 driver
    Enable3        var     PortD.3             ''Output Turns on Motor3 driver
    Enable4        var     PortD.4             ''Output Turns on Motor4 driver
    SinglePair     var     PortD.7             'Input Determines code path
    Input1         var     PortB.0             'PWM0
    Input2         var     PortB.1             'PWM1
    Input3         var     PortB.2             'PWM2
    Input4         var     PortB.3             'PWM3
    LCD            var     PortD.5
    Duty1          Var     Word
    Duty2          Var     Word
    Duty3          Var     Word
    Duty4          Var     Word
    Duty1S         data    word      00300
    Duty2S         data    word      00300
    Duty3S         data    word      00300
    Duty4S         data    word      00300
    BCD1           var     byte
    BCD10          var     byte
    LowRate        var     word
    HighRate       var     word
    TotalRate      var     word
    DisplayTenths  var     word
    MotorCount     var     byte              'Tracks motorspeed input
    Mod1           var     byte              'Offset tracker to correct motorspeed
    Mod2           Var     Byte              'Offset tracker to correct motorspeed
    Mod3           var     byte              'Offset tracker to correct motorspeed
    Mod4           Var     byte              'Offset tracker to correct motorspeed
    PosMin1        var     bit
    PosMin2        var     bit
    PosMin3        var     bit
    PosMin4        var     bit
    HighTime1       var     word
    LowTime1        var     word
    HighTime2       var     word
    LowTime2        var     word
    HighTime3       var     word
    LowTime3        var     word
    HighTime4       var     word
    LowTime4        var     word
    TotalTime1     var     word
    TotalTime2     var     word
    TotalTime3     var     word
    TotalTime4     var     word
    Freq           var     word
    UpperLimit     VAR     WORD
    LowerLimit     VAR     WORD
    Gain           var     word
    Subtract       var     bit
    Prefix          con      $FE             ' needed before each command
    LcdCls          CON      $51             ' clear LCD (use PAUSE 5 after)
    LcdLine1        CON      $00             ' move cursor to line 1
    LcdLine2        con      $40             ' move curson to line 2
    LcdLine3        con      $14             ' move curson to line 3
    lcdLine4        con      $54             ' move curson to line 4
    LcdCol1         con      $00             ' move cursor to column 1
    LcdCol2         con      $07             ' move cursor to column 7
    Backlight       con      $53             ' Backlighting 1-8
    CursorPS        con      $45             'Cursor Position
    CursorOn        con      $47             'Cursof On
    CursorOff       con      $48             'Cursor Off
    INTCON = 0            'Interrupts off for now
    INTCON2.7 = 1         'Pull Ups disabled
    ADCON0 = 0            'A/D OFF
    ANSEL0 = %00000000    'All analogue channels to digital
    ANSEL1 = %00000000    'All analogue channels to digital
    TRISA = %111111       'PortA to inputs
    TRISB = %00100000     'PortB to outputs, except B5
    TRISC = %00000110     'PortC, Switch3 and Switch4 outputs; Motorspeed and Population inputs
    TRISD = %00000000     'PortD, Switch 1 output; Enable1-4
    TRISE = %011
    PWMCON0=%01111111     'All odd PWMs enabled, all independent
    SSPCON=%00000000      'Disables Serial Port
    PTCON0 = %00001000                                              '8914 9140 2050
    'PTCON0 = %00000010 back up
    Freq=%11111111
    PTPERL =Freq.LowByte              '
    PTPERH =Freq.HighByte             ' PTPER = $0100 or 256d for ~19.45kHz
    PWMCON1 = 1             ' updates enabled, overrides sync w/timebase
    PTCON1 = %11000000      ' PWM time base is ON, counts up  500hz
    FLTCONFIG = %00000010   ' enable fault A, cycle-by-cycle mode
    'These variables are declared by the incPID routine but
    'the user needs to assign values to them.
    pid_Kp = $0700                     'Set Kp to 7.0
    pid_Ki = $0080                     'Set Ki to 0.5
    pid_Kd = $0225                     'Set Kd to 2.14
    pid_Ti = 4                         'Update I-term every 8th call to PID
    pid_I_Clamp = 10                  'Clamp I-term to max ±100
    pid_Out_Clamp = 10000             'Clamp the final output to ±511
    Serout2 LCD, 84, [Prefix,LcdCLS]
    'pause 1000
    SEROUT2 LCD,84, [Prefix,CursorPS,0, "Graham Electric Planter Drive "]
    High Enable1
    High Enable2
    High Enable3
    High Enable4
    MotorCount = 1
    read 0,Duty1.LowByte
    read 1,Duty1.HighByte
    read 2,Duty2.LowByte
    read 3,Duty2.HighByte
    read 4,Duty3.LowByte
    read 5,Duty3.HighByte
    read 6,Duty4.LowByte
    read 7,Duty4.HighByte
    PDC0L = Duty1.LowByte
    PDC0H = Duty1.HighByte
    PDC1L = Duty3.LowByte
    PDC1H = Duty3.HighByte
    PDC2L = Duty2.LowByte
    PDC2H = Duty2.HighByte
    PDC3L = Duty4.LowByte
    PDC3H = Duty4.HighByte
    pause 2000
    LowerLimit=200
    UpperLimit=800
    'Gain=10
    RunAround:
    Gosub BCD
    'SEROUT2 LCD,84, [Prefix,CursorPS,84,#bcd1," ",dec5 pid_Error]
    'SEROUT2 LCD,84, [Prefix,CursorPS,0, #BCD1, " ", #TotalRate, " ", #MotorCount]
    If BCD1 = 0 then                    'Tests row control with motor speed at 50%
      Duty1=300
      Duty2=300
      Duty3=300
      Duty4=300
      gosub RowControl
      GoSub MeasureRPM
      'GosuB AdjustRPM
    If BCD1 = 1 then                    'run time%" RunTime ", #MotorCount," ",
      SEROUT2 LCD,84, [Prefix,CursorPS,0, #motorcount," ",  #Duty1," ", #Duty2," ", #Duty3," ", #Duty4 ]
      gosub RowControl
      GoSub MeasureRPM
      GosuB AdjustRPM
    'If BCD1 = 1 then
    '  GoSub MeasureRPM
    '  gosub Display1
    '  If MotorCount = 4 or Motorcount >4 then
    '    MotorCount = 1
    '  else
    '    MotorCount = MotorCount + 1
    '  endif
    'endif
    If BCD1 = 2 then
      GoSub MeasureRPM
      gosub Display2
        MotorCount = 1
    If BCD1 = 3 then
      GoSub MeasureRPM
      gosub Display3
        MotorCount = 1
    If BCD1 = 4 then
      GoSub MeasureRPM
      gosub Display4
        MotorCount = 1
    If BCD1 = 5 then
       SEROUT2 LCD,84, [Prefix,CursorPS,0, "1 2 3 4 P"]
       SEROUT2 LCD,84, [Prefix,CursorPS,64, #OnOff1," ", #OnOff2," ",#OnOff3," ",#OnOff4," ", #Population]
       Low Switch1
       Low Switch2
       Low Switch3
       Low Switch4
    If BCD1 = 15 then
    goto RunAround
    AdjustRPM:                                 '50286 15586 34700
    If TotalRate = 0 then                       '2510 15586 52460  65536
      Duty1 = 0
      Duty2 = 0
      Duty3 = 0
      Duty4 = 0
    Select case MotorCount
     Case 1
      If OnOff1 = 1 then       ''''''''CHECK WHY NOT REDUCING DUTY
    '    If TotalRate>TotalTime1 then
          pid_Error =  TotalRate-TotalTime1     'Calculate the error
    '      Subtract = 0
    '      else
    '      pid_Error =  TotalTime1-TotalRate     'Calculate the error
    '      Subtract = 1
    '   endif
        Gosub PID
        SEROUT2 LCD,84, [Prefix,CursorPS,84,#bcd1," ",#pid_Sign, " ",dec5 pid_Out," ", #pid_Out_Clamp]
        pause 10000                         'Result returned in pid_Drive
        'If pid_Out.15 Then pid_Out = 0                             '
        Duty1 = pid_Out
     Case 2
      If OnOff2 = 1 then
        If TotalRate > TotalTime2 then
          If Duty2>LowerLimit then
           Duty2 = Duty2-Gain
        If TotalRate < TotalTime2 then
          If DUty2 < UpperLimit then
           Duty2 = Duty2+Gain
     Case 3
      If OnOff3=1 then
        If TotalRate > TotalTime3 then
          If Duty3>LowerLimit then
           Duty3 = Duty3-Gain
        If TotalRate < TotalTime3 then
          If DUty3 < UpperLimit then
           Duty3 = Duty3+Gain
     Case 4
      If OnOff4=1 then
        If TotalRate > TotalTime4 then
          If Duty4>LowerLimit then
           Duty4 = Duty4-Gain
        If TotalRate < TotalTime4 then
          If DUty4 < UpperLimit then
           Duty4 = Duty4+Gain
     end select
    MeasureRPM:
      pulsin Population, 0, LowRate
      pulsin Population, 1, HighRate
      TotalRate= LowRate+HighRate
      SEROUT2 LCD,84, [Prefix,CursorPS,20,#TotalRate," "]
      If MotorCount = 1 then
        If Onoff1 = 1 then
          High Switch1
          Low Switch2
          Low Switch3
          Low Switch4
          PUlsin Motorspeed, 1, HighTime1
          Pulsin Motorspeed, 0, LowTIme1
          If HighTime1>500 then
            If LowTime1>500 then
              TotalTime1 = HighTime1+LowTime1
              'else
              'TotalTime1 = 0
          SEROUT2 LCD,84, [Prefix,CursorPS,64,Dec5 TotalTime1," ",Dec5 HighTime1," ",Dec5 LowTIme1, " " ]
          'SEROUT2 LCD,84, [Prefix,CursorPS,10, #Duty1," " ]
      Endif
      If MotorCount = 2 then
        If Onoff2 = 1 then
          Low Switch1
          High Switch2
          Low Switch3
          Low Switch4
          PUlsin Motorspeed, 1, HighTime2
          Pulsin Motorspeed, 0, LowTIme2
          If HighTime2>500 then
            If LowTime2>500 then
              TotalTime2 = HighTime2+LowTime2
          SEROUT2 LCD,84, [Prefix,CursorPS,64,Dec5 TotalTime2," ",Dec5 HighTime2," ",Dec5 LowTIme2, " "]
          SEROUT2 LCD,84, [Prefix,CursorPS,10, #Duty2," " ]
      EndIf
      If MotorCount = 3 then
        If Onoff3 = 1 then
          Low Switch1
          Low Switch2
          High Switch3
          Low Switch4
          PUlsin Motorspeed, 1, HighTime3
          Pulsin Motorspeed, 0, LowTIme3
          If HighTime3>500 then
            If LowTime3>500 then
              TotalTime3 = HighTime3+LowTime3
          SEROUT2 LCD,84, [Prefix,CursorPS,64,Dec5 TotalTime3," ",Dec5 HighTime3," ",Dec5 LowTIme3, " " ]
          SEROUT2 LCD,84, [Prefix,CursorPS,10, #Duty3," " ]
       Endif
      If MotorCount = 4 then
        If Onoff4 = 1 then
          Low Switch1
          Low Switch2
          Low Switch3
          High Switch4
          PUlsin Motorspeed, 1, HighTime4
          Pulsin Motorspeed, 0, LowTIme4
          If HighTime4>500 then
            If LowTime4>500 then
              TotalTime4 = HighTime4+LowTime4
          SEROUT2 LCD,84, [Prefix,CursorPS,64,Dec5 TotalTime4," ",Dec5 HighTime4," ",Dec5 LowTIme4, " " ]
          SEROUT2 LCD,84, [Prefix,CursorPS,10, #Duty4," " ]
        MotorCount = 1
        write 0,Duty1.LowByte
        write 1,Duty1.HighByte
        write 2,Duty2.LowByte
        write 3,Duty2.HighByte
        write 4,Duty3.LowByte
        write 5,Duty3.HighByte
        write 6,Duty4.LowByte
        write 7,Duty4.HighByte
    Display1:
      If Motorcount = 1 then
        SEROUT2 LCD,84, [Prefix,CursorPS,64,DEC5 LowTime1]
        SEROUT2 LCD,84, [Prefix,CursorPS,20,DEC5 HighTime1 ]
        SEROUT2 LCD,84, [Prefix,CursorPS,84, #TotalTime1]
    Display2:
      If Motorcount = 2 then
        SEROUT2 LCD,84, [Prefix,CursorPS,64,DEC5 LowTime2]
        SEROUT2 LCD,84, [Prefix,CursorPS,20, DEC5 HighTime2]
        SEROUT2 LCD,84, [Prefix,CursorPS,84, #TotalTime2]
    Display3:
      If Motorcount = 3 then
        SEROUT2 LCD,84, [Prefix,CursorPS,64,DEC5 LowTime3 ]
        SEROUT2 LCD,84, [Prefix,CursorPS,20,DEC5 HighTime3]
        SEROUT2 LCD,84, [Prefix,CursorPS,84, #TotalTime3]
    Display4:
      If Motorcount = 4 then
        SEROUT2 LCD,84, [Prefix,CursorPS,64,DEC5 LowTime4 ]
        SEROUT2 LCD,84, [Prefix,CursorPS,20,DEC5 HighTime4]
        SEROUT2 LCD,84, [Prefix,CursorPS,84, DEC5 TotalTime4]
    RowControl:
      If Onoff1 = 1 then
         high enable1
         low enable1
      If Onoff2 = 1 then
         high enable2
         low enable2
      If Onoff3 = 1 then
         high enable3
         low enable3
      If Onoff4 = 1 then
         high enable4
         low enable4
    BCD:
    BCD1=PORTA
    BCD1=BCD1 & $0F
    BCD1=BCD1^ $0F
    'BCD10=PORTC
    'BCD10=BCD10 & $F0
    'BCD10=BCD10^ $F0
    'BCD10 = BCD10 >>4
    BCD10=PORTC
    BCD10=BCD10 & $0F
    BCD10=BCD10^ $0F
    'On Start-Up
    'Check SinglePair
    '   If High Then goto Single
    '   If Low then goto Paired
    'Single
        'If OnOff1 = 0 then Enable1 = 0 else Enable1=1
        'If OnOff2 = 0 then Enable2 = 0 else Enable1=2
        'If OnOff3 = 0 then Enable3 = 0 else Enable1=3
        'If OnOff4 = 0 then Enable4 = 0 else Enable1=4
        'Measure DutyCycle of Population
        'Measure Motor1-4 rpm
        'Adjust Input1-4 dutycycle to maintain speed requested from Population
    'GOto Single
    'Paired
        'Calculate offset needed for requested Population
        'Measure motor1 rpm
        'Adjust Input1 dutycycle to maintain speed requested from Population
        'Measure offset between motor1 and motor2
        'Adjust Input2 dutycycle to get required offset
    'Goto Paired
    '  Duty1 = (LowRate*10)/492      '10%    489
    '  Duty2 = (LowRate*10)/492      '20%    977
    '  Duty3 = (LowRate*10)/492      '50%    2461
    '  Duty4 = (LowRate*10)/492      '80%    3924
    '  Duty1 = Duty1*10
    '  Duty2 = Duty2*10
    '  Duty3 = Duty3*10
    '  Duty4 = Duty4*10
    '  PDC0L = Duty1.LowByte
    '  PDC0H = Duty1.HighByte
    '  PDC1L = Duty3.LowByte
    '  PDC1H = Duty3.HighByte
    '  PDC2L = Duty2.LowByte
    '  PDC2H = Duty2.HighByte
    '  PDC3L = Duty4.LowByte
    '  PDC3H = Duty4.HighByte
     ' DisplayTenths=Duty1-(Duty1/10*10)
      'SEROUT2 LCD,84, [Prefix,CursorPS,10,#TotalRate]
    Last edited by Darrel Taylor; - 20th March 2011 at 16:48. Reason: Fixed HTML problem
    Hi Tobias,
    In the code you posted, which still doesn't show properly on the forum, you have the IF pid_Out.15 THEN pid_Out = 0 line commented but I'm sure that's not the case in the compiled and tested code?
    And, as far as I can see the only thing you have "connected" to the output of the PID filter is the DUTY1 variable, I don't see how that connects to DUTY4 - if that was the purpose.
    Finally, you said earlier that you're trying to control the speed of 4 motors based on the speed of anoter motor. The PID filter will only work with ONE motor. You are not going to be able to have one PID filter for each motor with this code. If that is what you need (but I'd get ONE working first) then there is a special version available that allows multiple filters to be run.
    I'm sorry I'm not not much of a help here but I still haven't got the whole picture of exactly what you're trying to do. What I'd probably do is try to boil it down to the bare minimum in order to get a grip on how it works.
    Also, Darrel pointed out a thing about the DEFINEs that I don't see in your posted code either.