Turning a smoke machine on/off with a triac


Closed Thread
Results 1 to 6 of 6

Hybrid View

  1. #1
    Join Date
    Jun 2007
    Location
    Mansfield, UK
    Posts
    697


    Did you find this post helpful? Yes | No

    Default

    Ok, Thanks. I will go with the triac then. I'm using BTA already so thats good.

    I did think about using a relay but I've used those in the past for the pump motor and they cause all nearby PICs to reset (I had a post on here a few years ago about it). The solution was to use triacs. I've used diodes in the past on the low voltage side of relays to stop current flowing backwards. Maybe something like that on the high voltage side would fix the problem but I would rather use a triac instead.

  2. #2
    Join Date
    Oct 2004
    Posts
    448


    Did you find this post helpful? Yes | No

    Default

    A triac would be fine. Even better, add a few lines to detect the zero crossing, and switch on right after that. That should reduce the inrush current.

    Regards,

    Anand

  3. #3
    Join Date
    Jun 2007
    Location
    Mansfield, UK
    Posts
    697


    Did you find this post helpful? Yes | No

    Default

    Good idea. I have at least 1 pin spare on the PIC. I'll do the same for the pump too

  4. #4
    Join Date
    Feb 2003
    Posts
    432


    Did you find this post helpful? Yes | No

    Default

    Quote Originally Posted by ardhuru View Post
    A triac would be fine. Even better, add a few lines to detect the zero crossing, and switch on right after that. That should reduce the inrush current.

    Regards,

    Anand
    Or drive the triac with an opto isolator that includes zero crossing detection.
    Keith

    www.diyha.co.uk
    www.kat5.tv