    not as interesting as a pic ckt,
    but for about 10 to $15, you can get an adjustable delay on break cube type relay, that just hooks in series with the compressor run relay coil (2 terminal device) and protects the comp from short-cycling every time power is removed.
    don
    amgen

  2. #2
    Join Date
    Aug 2005
    Location
    Houston, TX
    Posts
    43


    Did you find this post helpful? Yes | No

    Default Re: 24v ac delay


    I didn’t find any relays for $10 –$ 15 which would delaystart up when all power is out but I did find an Omeron G3VM61A1 solid state two pole single throw relay rated for 60 Vac/dc, 500 ma for $2.15 (Mouser.)The A/C compressor relay drawsless than 300 ma at 27 volts AC, so there is plenty of headroom. I added a snubber circuit for protection fromthe compressor relay coil.

    I spent more time I care to admit trying to figure out howto sense a power out condition, when the power was out, without batteries. Thenit dawned on me that all I needed to do was wait until power is restored, have along start up process in a PIC, and then send a pulse to a latching relay. I use the second pole of the above SS relay tolatch it on. When the power goes out,the relay opens, and must wait for a pulse from the PIC to close again. I use 3pins to select the delay time with a jumper, 4, 4 ½, or 5 min.

    So far it works fine. It has been tested by 4 actual poweroutages and several 2-3 second power “blinks.”

  3. #3


    Did you find this post helpful? Yes | No

    Default Re: 24v ac delay

    sounds like a good circuit, does it always add a delay when starting the compressor ? sometimes thats annoying waiting for cooling.
    for future reference,

    http://acsuperstore.com/Merchant2/4....alog/c605.html

    I use to use these alot when I was working...

  4. #4
    Join Date
    Aug 2005
    Location
    Houston, TX
    Posts
    43


    Did you find this post helpful? Yes | No

    Default Re: 24v ac delay

    Correction, the relay I use is a G3VM-62C1. It costs $3.19, quite a bargin I think.

    And yes, it always delays a restart after the power goes out, but only after the power goes out. As long as to power is on, the relay stays latched. The thermostat will not restart faster than 4 - 5 minutes on its own, but it has no provision for delay after a power loss.

  5. #5
    Join Date
    Aug 2005
    Location
    Houston, TX
    Posts
    43


    Did you find this post helpful? Yes | No

    Default Re: 24v ac delay

    One more item re the generator. I want to know when it is running. A little Rf remote system seemed the way to go, but I had to sense when the unit was running. Since it is an emergency unit, I did not want to tap its electrical system, for fear a short would would mess it up, or might affect the warranty.

    My solution was to mount a reed switch near the alternator which controls power for a battery powered pic controlled transmitter. The receiver is in the house, mounted in a hollow book I got at a hobby store. It works great so far.
    Last edited by Archangel; - 23rd August 2011 at 04:20.

  6. #6
    Join Date
    Jan 2005
    Location
    Montreal, Quebec, Canada
    Posts
    3,159


    Did you find this post helpful? Yes | No

    Default Re: 24v ac delay

    Moved from Schematic.

    Robert