Hi, Im making a circuit that runs from a PCB transformer. Is it possible to connect the circuit ground after being rectified to the mains earth wire? The circuits use RS485 and im hoping to save on wiring
Hi, Im making a circuit that runs from a PCB transformer. Is it possible to connect the circuit ground after being rectified to the mains earth wire? The circuits use RS485 and im hoping to save on wiring
I take it you are trying to save a ground wire in the rs485 link and intend to use mains earth as the common reference...
Personally I would leave the "secondary side" floating to prevent any earth current loops. I would however use a Screened cable or an additional 0v reference line to complete the 3 wire link required by RS485.
Tim.
I see, Im going to use twisted pair for A and B but not screened. Ill keep the 0V reference wire though.
Thanks for your help