    Older RS485 driver ICs (e.g. 75176) can only do 32. Newer drivers (e.g. ST485) can do as many as 256.

  2. #2
    Join Date
    Nov 2003
    Location
    Greece
    Posts
    4,170


    Did you find this post helpful? Yes | No

    Default

    check the data sheets of the device you will use. If the input of the RS-485 receiver puts high load on the lines then node number is limited (up to 32 for the RS-485 specs).

    Newer devices like form analog devices (http://www.analog.com/en/interface/r...cts/index.html) present minimum load on the lines so up to 256 nodes can be implemented.

    Ioannis

  3. #3
    Join Date
    Nov 2008
    Posts
    48


    Did you find this post helpful? Yes | No

    Default

    Ah, sorry, was a misunderstanding from me,
    thoght you have restrictions with the addresses...

  4. #4
    Join Date
    Jun 2006
    Posts
    40


    Did you find this post helpful? Yes | No

    Default

    Thanks for the information. Get better understanding.
    1. If i still use 75176, do you think the attach circuit will work ?

    2. Do you think if should isolate the line as in the attachment if the wiring goes so long ? ( could have trouble with terminal resistance or isolation of fault )

    3. Most of the articles i gone through does not mention the actual type of cable to be used except twisted pair. In order to determine terminal resistor value, i need to know the cable impedance. What if i do not have the information ? Will 120ohm resistor still helps. Or it is better to use 120 ohm with shorter distant cable but i can add isolator to extend the communication line ?
    Cheers,

    mychangl
    "The Dream Is Everything"

  5. #5
    Join Date
    Jun 2006
    Posts
    40


    Did you find this post helpful? Yes | No

    Default

    Ooops, i missed out the diagram..
    Attached Images Attached Images  
    Cheers,

    mychangl
    "The Dream Is Everything"

  6. #6
    Join Date
    Nov 2003
    Location
    Greece
    Posts
    4,170


    Did you find this post helpful? Yes | No

    Default

    How long is "long"?

    Do you really need isolation?

    As for cable, I always use UTP cable. It is twisted and has characteristic impedance very close to 120 ohms.

    If you don't have a copy of the Serial Port Complete by Jan Axelson, you must get it soon.

    Lastly for short distances and low baud rate (less than 9600), termination is not really necessary.

    Ioannis

  7. #7
    Join Date
    Jun 2006
    Posts
    40


    Did you find this post helpful? Yes | No

    Default

    I will use baud rate of 9600. Total distance is estimated 500 meters since i cannot use star topology.

    You use UTP, it is unshield - is it okay ? how about other noise ?

    I am thinking that, may be isolation can localize the fault in case it happen.

    Regards
    Cheers,

    mychangl
    "The Dream Is Everything"

Similar Threads

  1. RF sensor network
    By Ron Marcus in forum mel PIC BASIC Pro
    Replies: 10
    Last Post: - 21st September 2006, 01:07
  2. RS 485 wireless communication
    By Armadus in forum mel PIC BASIC Pro
    Replies: 22
    Last Post: - 26th January 2006, 20:30
  3. RS485 - ibutton network
    By ccsparky in forum mel PIC BASIC Pro
    Replies: 7
    Last Post: - 6th June 2005, 22:48
  4. Slave Databuffer - RS-485 network
    By DynamoBen in forum mel PIC BASIC Pro
    Replies: 4
    Last Post: - 1st June 2005, 19:36
  5. RS 485 using 16F84A
    By ngeronikolos in forum mel PIC BASIC Pro
    Replies: 1
    Last Post: - 18th May 2005, 15:46

Members who have read this thread : 1

You do not have permission to view the list of names.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts