COUNT is not counting again
My excerpted code as listed below all works until it gets to the point where it is suppose to count the input pulses to pin RA1 during each loop of a REPEAT...UNTIL epoch and write the count valuable to a variable Cin. Then the accumulated count for all epochs is incremented for each epoch by adding Cin to i. The accumulated count is then suppose to be written to EEPROM after the accumulated count reaches its limit and exits the loop.
I know the loop is working because I see the LED blinking on each loop and because the WRITE statement is actually writing over the FF value in EEPROM. However, the Cin value that is written is always zero (0), indicating that COUNT is actually not counting. Therefore, the loop is never exiting, because i=i+Cin is always zero and the WRITE 7,i statement is therefore never executed. For the life of me I can't figure out why this is happening.
I had a similar problem when I first wrote this code and solved the problem by adding the missing ANSEL =0 and ANSELH = 0 statements, which are in this code now, so that can't be the problem. I checked my register settings and I can see no reason why COUNT is not counting. Can anyone see what is wrong?
' -----[ Title ]-----------------------------------------------------------*
' File...... Toilet_Meter.BAS *
' Compiler.. PICBASIC PRO Compiler from microEngineering Labs *
' Purpose... PIC16F690 microcontroller for Toilet Meter Project *
' Author.... John R. Ellis, *
' Started... 2/20/2009 *
' Updated... Version 1.0.6 on 5/2/2009 *
' Program Size: 255 Words * *
' -----[ Program Description ]---------------------------------------------*
' This Program is for a PIC16F690 installed in a PICkit2 Starter Kit *
' Purpose:
' 1) Monitor an input for an external Interrupt from flush *
' 2) On Interrupt, command latching solenoid to open valve *
' 3) Measure flow meter output to determine when 1.6 *
' gallons have passed *
' 4) On 1.6 gallons, command latching solenoid to close *
' 5) Put Microcontroller back in Sleep State to await next *
' Flush Interrupt *
' This Program uses the PIC16F690 to control a solenoid operated water valve
' and to measure the volume of water flowing through a flow meter.
' This program places the MCU in sleep mode most of the time until it receives
' an interrupt from the activation of the toilet flush handle that closes a
' contact limit switch that grounds an input pin of the microcontroller as an
' interrupt. I/O pin connections to the PIC16F690 are as follows:
' RA1...is connected as an input from the meter to count pulse inputs, which
' are simulated by multiple manual depressions of a switch on the PICKIT2
' demo board during program testing.
' RA3...is connected as an interrupt input from the FLUSH contact limit Switch.
' RC0...is connected as an output to an LED and is slowly flashed when the valve
' is open. It is also flashed even more slowly when the battery is low.
' RC3...is connected as an output to the latching solenoid that opens or
' closes the valve. During program testing with the PICkit2 demo
' board it is connected to an LED to show when the pulse is sent.
' -----[ Device Declaration ]----------------------------------------------
'@device pic16F690, intrc_osc_noclkout, BOD_OFF, PWRT_OFF, wdt_off,mclr_off,
' protect_off
' -----[ Revision History ]------------------------------------------------
' -----[ Variables Initialization ]----------------------------------------
k CON 15 ' Calibration factor for flow meter...# pulses per gal
i VAR Byte ' Index used in Gallon counter Repeat...Until loop
Cin VAR Byte ' Storage variable for count from COUNTER
' -----[ Initialization ]--------------------------------------------------
'Registers Settings
Init:
ADCON1 = %01110000 ' Set PORTA to digital I/O & FRC (clock derived from a
' dedicated internal oscillator)
TRISA = %00000010 ' Set all PORTA pins except RA1 to outputs
TRISB = %00000000 ' Set all PORTB and PORTC pins to outputs
TRISC = %00000000
PORTC = %00000000 ' Pre-set PORTB pins low, turning LEDs off
ANSEL = 0 ' Set PortA to digital I/O; Unselect any of the A/D channels
ANSELH = 0
TRISA.1 = 1 ' Set RA1 as input port for meter pulse inputs
PortA.1 = 0 ' Pre-set RA1 at Low value
INTCON = %10010000 ' Set INTCON register to enable interrupts
' -----[ Main Code ]-------------------------------------------------------
MAIN:
'Send PWM pulse to latching solenoid to open valve
'Generates 10 millisec pulse on RC3 output pin
LOW PORTC.3 ' Initialize output pulse polarity
PULSOUT PORTC.3,1000 ' Generate 10 msec pulse to RC3
' Valve should be open at this point and water flowing
' Start measuring output of flow meter at RA1 input pin
Cin = 0 ' Initialize pulse count variable to zero
i = 0 ' Initialize total pulse count index to zero
REPEAT ' Assume it takes k accumulated pulses for required gallons
' Count the number of pulses from Hall Effect Magnetic Sensor in 5 sec
' epochs and add count from each epoch to total accumulation and then
' shutoff the valve when count meets i>k criteria.
Count PORTA.1,5000,Cin
WRITE 5,Cin ' Write count into EEPROM location 5 during
' pre-production testing
'Slowly blink LED during water flow
HIGH PORTC.0 ' If we get here, Blink the LED once
PAUSE 100
LOW PORTC.0
i = i + Cin ' Add count to total pulse accumulation indexer
'When i >= k, required gallons have flowed by the meter
UNTIL i = k
WRITE 7,i 'Store result as test of code..not in production
'Write 8,i.LowByte
GoTo ShutValve
ShutValve: 'Send PWM pulse to latching solenoid to close valve
PULSOUT PORTC.3,1000 ' Generate required 10 msec pulse to RC3
' Valve should be closed at this point and no water flowing
COUNT isn't counting again
Darrell,
Thanks for the reply. I commented out the INTCOM statement and the program still runs as I was describing above, but still doesn't count input pulses.
As far as missing pulses, the rate at which the incoming pulses occur is much, much slower than the loop rate, so I don't think it will miss that many pulses.
At any rate, I will look into how to do this with interrupts, but I still would like to figure out why the COUNT statement is not counting. Any ideas??
Joe and Bruce, thanks for the excellent inputs! I didn't totally grasp Joe's suggested use of the TMR0 as a counter, mainly because the wiring on microcontroller board doesn't enable me to use RA0 to generate a clock input to RA2 as Bruce's approach suggests.
However, I have gone back to the drawing board to try to count the input pulses from the external sensor by counting them as interrupts. I am enclosing my new code below for reference. I tried to set up the Int-Handler to test for either a RA2/INT or a RA1 on change interrupt by means of two IF_Then blocks. Unfortunately it doesn't appear to recognize any interrupts. I know this because I inserted a LED blink at the very start of the Int_handler to tell me when an interrupt has been recognized and it never blinks for either a RA2/INT or a RA1 on change interrupt. If the RA1 interrupt is received it would increment an index counter, i, for each pulse. I also put the write statement in the If_Then block for RA1 on change interrupt so I could use the PICkit2 to read the EEPROM memory address for the value and it never changes from the FF value. These two tests tell me that my interrupt handler isn't working. Can anyone tell me what I have done wrong from this code??
' -----[ Device Declaration ]--------------------------------------------------*
@device pic16F690, intrc_osc_noclkout, wdt_off, mclr_off, protect_off
' -----[ Variables Initialization ]--------------------------------------------*
k CON 15 ' Calibration factor for flow meter = # pulses per gal
' -----[ Initialization of Registers ]-----------------------------------------*
'Register Settings
TRISA = %00001010 ' Set PORTA pins RA1 and RA3 to inputs, others as outputs
TRISB = %00000000 ' Set PORTB pins as outputs
TRISC = %01000000 ' Set PORTC pin RC6 to input, all others as outputs
PORTC = %0000000 ' Pre-set PORTC LED pins low, turning LEDs off
'A/D & Comparators disabled
ANSEL=0 ' Set PortA to digital I/O
ANSELH=0 ' Analog module disabled
CM1CON0=0
CM2CON0=0
TRISA.1 = 1 ' Set RA1 as input port for simulated meter pulse inputs
TRISA.3 = 1 ' Set RA3 as Master Reset input port
PORTA.1 = 1 ' Pre-set RA1 at High value
' Setup Interrupts
INTCON = %10011000 ' Enable RA2/Int external interrupt and PORTA interrupts on
' change
IOCA = %00000010 ' Enable RA1 for interrupt on change for pulses received
' from momentary switch, activation which simulates external HS1 sensor pulses
on interrupt goto Int_Handler
i=0 ' Initialize counter index to zero
' -----[ Main Code ]-----------------------------------------------------------*
MAIN:
INTCON = %10011000 ' Clear interrupt flags
IF i < k Then 'k is 15 pulse threshold
' Keep the valve open...do nothing..let water flow
Else
'i >= 15....1.6 gallons reached...Close the valve
GOTO Main 'Main program loops while waiting for RA1 on change interrupt to count pulses
Int_Handler:
Disable ' No interrupts past this point
'Blink LED on receipt of this interrupt
HIGH PORTC.0 ' Blink the LED once
PAUSE 100
LOW PORTC.0
If INTCON = %10011010 Then 'RA2/INT external interrupt received
PULSOUT PORTC.3,1000 ' Generate 10 msec pulse to RC3 to open valve
Endif
If INTCON = %10011001 Then ' Flow meter interrupt pulse received on PORTA
i = i + 1 'Increment pulse count value
WRITE 7,i 'Store updated count result
Resume ' Return to main program
Enable
Bruce, I really liked the code you posted for a Non-interrupt version to do my counting. I prefer it over the other options you posted, since I won't get into the problems I have seen in trying to handle interrupts in noisy signal envoirnments. It is concise with minimal executable statements, low memory requirement and should execute efficiently.
It looked to me like it should run with my PIC16F690 almost as is. So I set up a pinout so that my momentary push button switch that I have been using to simulate the external sensor pusles will connect the RA2 pin to ground each time I depress the switch. I presumed this would be enough of a "clock" transition to increment the TMR0 counter. However, I haven't yet been able to see it run since I am having a compile problem with assembler errors that I can't understand or trace. I am attaching a screen snapshot (.jpg image) that shows the errors in lower left. Can you clarify what these errors are telling me?
Bruce,
OK, I am using PBP compiler via MicroStudio that uses MSPM assembler. So I made the config change. Now I get a different, but single assembler error: " Error[118]: Overwriting previous address contents[2007]" When I click on it, it points to the @__config statement.
Again I don't know what this is telling me...can you advise.
BTW, is there anywhere that you can get error listings for the MSPM assembler so you know what they mean?
Bruce, I see now in 16F690 data sheet that for TTL the minimum Vih threshold is 2.0 volts and for Schmidt trigger it is 0.8 volts. Would my switch grounding interface appear to RA2 as TTL or Schmidt trigger? Since the RA2 input is 1.8 v when open and I am grounding it to create a simulated pulse, I don't know whether this is enough downward transition or not. If not, what can I do about it. I thought the open circuit voltage level of RA2 would be over 2.0 volts.
Bruce, I moved the TMR0 = 0 clear statement after the WRITE statement. However, that is not the problem. I can see while running the code that the TMR0 value is never exceeding the value of K so it never enters the ELSE block and therefore never gets to the WRITE statement which leaves the EEPROM address at inital value of FF continuously.
All this is telling me that my approach to simulating the input pulses by momentarily grounding the RA2 port with my switch closure is not triggering the TMR0 count, but not quite sure what to do about that...I don't yet have access to the meter so I can use real pulse inputs from the sensor.
I understand what you are saying about the threshold value for Vih. However, my 16F690 is running off 5.0 volts, so I would have expected the voltage at RA2 to be near 5.0 volts when the switch is open (not grounded). Yet what I see is 1.8 volts, which is obviously not enough for Vih. This doesn't make sense to me, but explains why the TMR0 value is not incrementing. Any ideas why the RA2 port voltage would be at 1.8 vdc rather than 5.0 vdc when it is unloaded?
I also didn't quite understnd your comments about RA5. My code is a close modification of the Non-interrupt version code you posted above and doesn't even mention RA5 (see current code posting below). Are you saying I have to use RA5 somehow in generating the "clock" input to RA2??
@ __config _INTRC_OSC_NOCLKOUT & _WDT_OFF & _MCLRE_OFF & _CP_OFF
K CON 15 ' Calibration factor for flow meter = # pulses per gal
' Setup Timer0 as an 8-bit counter with the clock input on RA2.
' 1:1 TMR0 prescaler
' TMR0 counts on high-to-low transitions
OPTION_REG = %00111000
' A/D & Comparators disabled
ANSEL=0 ' all digital
ANSELH=0 ' analog module disabled
CM1CON0=0
CM2CON0=0
' Port setup
PORTC = 0 ' LEDs off, PULSOUT RC3 provides a high-going pulse
PORTA = 0
TRISC = %11110000 ' lower 4 pins outputs
TRISA = %11111111 ' RA2 = 2TMR0 clock input for simulated meter pulse inputs
TMR0 = 0 ' clear TMR0 count
IF TMR0 < K THEN
HIGH PORTC.0 ' Light LED continuously while water is flowing
WRITE 7, TMR0 ' write before TMR0 cleared
Low PORTC.0 ' Blink LED on each clear after TMR0 >= K
PAUSE 500
HIGH PORTC.0
PAUSE 500
LOW PORTC.0
GOTO Main
Bruce, I may have stumbled onto part of my problem. I checked the switch interface more closely and discovered that the wire I was inserting into a female header that was connected to RA2 from the switch was not making good contact. Now when I check the voltage on RA2 pin when it is open output it reads 3.2 vdc. Still a long ways from VDD or Vih, but yet when I now depress the switch I am getting TMR0 count values. However, I notice that only 3-4 depressions of the switch causes TMR0 to obviously exceed the K value and trigger the ELSE block where it is written to memory and then cleared. I presume that this means there is a lot of switch bounce on the momentary switch depressions, each bounce being counted as a pulse by TMR0. Yet I can't figure out why it even works when the RA2 voltage transitions are only from 3.2 volts to ground. Any ideas?
Maybe Interrupts would still be the better approach to do the counting, where the interrupt would trigger on the first switch closure and should ignore the switch bounces while further interrupts are disabled during the Int-handler. What do you think?
Joe, I enabled a WPUA.2 = 1 on RA2. However, with this change the voltage on RA2 when open circuit output is still at 3.2 vdc rather than Vih or close to Vdd. My code now looks like below. Interestingly the WRITE 7, TMR0 in the IF block never shows a value other than zero. However, just a couple of momentary switch activations will enter into the ELSE block where the WRITE 9, TRM0 statement shows a value of greater than K each time. So it looks like a lot of switch bounce going on, but the thing I don't understand is why the WRITE 7, TMR0 statement isn't showing any TMR0 values< K.
I also notice that if I comment out the LED blink statements in the IF block, the WRITE 7 statement doesn't write anything because the memory address shows a continuous FF value. Strange things that I don't understand. But at least it looks like the TMR0 is counting whether the value shows up correctly or not.
Tomorrow I am going to try to generate another method of simulating the external sensor input pulses to eliminate the switch bounce problem. I thought this might be possible by using one of the I/O pin outputs in a similar blink sequence loop as I am using for the LED, and then route that output into RA2. Do you think this would work? I will try to use one of the I/O pins that has a CMOS output.
This time with the code:
CM1CON0=0
CM2CON0=0
' Port setup
PORTA = 0
WPUA.2 = 1 ' enable weak pull-up on RA2
IF TMR0 < K THEN
WRITE 7, TMR0 ' write count during testing
HIGH PORTC.0 ' Blink Light LED while water is flowing
Pause 500
LOW PORTC.0
PAUSE 500
WRITE 9, TMR0 ' write count during testing before clearing
GOTO Main
mister_e
FYI, there's a new DEFINE for that
I don't see this DEFINE listed in Appendix B of the PICBASIC PRO manual, which supposedly lists all DEFINEs.
Can you explain how you would use this to replace the code statements Joe lists to mask interrupts while writing? Do you just precede the WRITE statement with DEFINE WRITE_INT1? After the WRITE, do you still have to re-enable the interrupt? I guess if you have to do all this, I don't see how it is any more efficient than using Joe's 4 statements.
PROBLEM SOLVED ON THIS THREAD.
Thanks, Bruce, for clarification on DEFINE. I will use this in all future programs where I have write statements.
Joe S., the 0.01 uF capacitor definitely solved my switch bounce problem. The code now works perfectly and always counts exactly 15 pulses when it activates the external pulse to the valve solenoid.
Your guys are stupendous! I learned more in the interchanges during this thread about programming PIC MCUs than I have learned in weeks reading different sources.
Thanks again and keep up the good work!
Now same working code won't work with PCB Pro??
I thought I had this problem licked. Then I purchased PCB PRO and tried to run the same code that ran in PCB. I get all an "Overwriting prrevious address contents" assembly error and many "Symbol not previously defined erros" as related to the ANSEL, ANSELH, CM1CON and CM2CON statements as shown in the attached image. These errors sort of sound like a problem with the CONFIG statement not being commented out in the .inc file. I did make sure I commented out the @ __device statement in the 16F690.incl file that came with PCB PRO so it isn't overwritten by the !__config statement in the code.
Can't figure thwhy this code now won't assemble. Can any of you advise me why my code would run in PCB and won't assemble in PCB PRO??
Here is the current code as adapted from Bruce's "Non-Interrupt version" in his above post.
i var Byte ' Indexer for use in For..Next loop
CM1CON0=0
CM2CON0=0
' Port setup
PORTA = 0 ' Clear the port register latches
PORTB = 0
' Set or clear the data direction registers
TRISA = %11111111 ' RA2 = TMR0 clock input for simulated meter pulse inputs
TRISB = %11111111
'VRCON = %00000000 ' turns the Vref Module OFF by clearing bit 7, 6, 4
IF TMR0 < K THEN
PULSOUT PORTC.3,1000 ' Generate required 10 msec pulse to RC3..close valve
DEFINE WRITE_INT 1
WRITE 7, TMR0 ' write count if you need to during testing
TMR0 = 0 ' Clear timer count
For i = 1 to 3 ' Blink LED 3x to indicate valve turned off
HIGH PORTC.0
PAUSE 500
LOW PORTC.0
Next
GOTO Main ' Loop to Main to wait for next meter flow input
Path was the problem...now I have a new problem
Bruce
"Make sure your path statement includes information on where you have MPLAB installed, or modify the 16F690.INC file to point directly to it."
I guess when I upgraded to PB Pro and installed it, MPLAB must have ended up in a different place. Thanks for catching this...I could have spent a long time looking and not thinking of this.
Now I have a different problem. Although I was going to try to do the counting with a NonInterrupt version of using the TMR0 overflow counter as you described above, I discovered as I progressed on my app design that I really need to do the counting with an interrupt and also another interrupt for checking on an external switch closure. I therefore am trying to use the below code where I have the interrupt handler doing two IF..THEN checks of the flag bits to handle either the TMR0 overflow while using RA2 input to TMR0 as switch for counting, or the RABIE on-change-interrupt for the RA3 input from a switch closure to ground. The TMR0 interrupt works in this code, however, the RABIE on-change-interrupt does not. I can't figure out why. Can you see whay the RABIE isn't working??
' -----[ Variables & Aliases Intitialization ]-----------------------------
led1 VAR PORTC.0 ' Set RC0 as LED indicator of valve open..water flowing
led2 VAR PORTC.1 ' Set RC1 as LED indicator of low battery
valve VAR PORTC.3 ' Set RC3 as valve solenoid open/close command
low_bat VAR PortA.0 ' Set RA0 as battery low power monitor
meter VAR PORTA.2 ' Set RA2 as input for Hall Sensor meter pulse Interrupt
flush VAR PORTA.3 ' Set RA3 as input for sensing flush switch closure Int
bat_mon VAR Byte ' bat_mon value when Vtrh multiplied by low_bat
' -----[ Constants Initialization ]----------------------------------------
k CON 10 ' Calibration factor for flow meter...# pulses per gal
i VAR Byte ' Index used in Gallon counter loop
Vthr CON 4 ' Low Battery Monitor threshold
'EEPROM PRESETS
'DATA @0,0
'OSC DEFINE
'DEFINE OSC 4
'Register Settings
Init:
TRISA = %11111111 ' Set all PORTA pins to inputs...RA0, RA2 & RA3 are used
TRISC = %00000000
PORTC = %00000000 ' Pre-set PORTC pins low, turning LEDs off
TMR0 = 256-K ' Preload TMR0 to overflow after k counts
ADCON0 = %01110000 ' Set PORTA to digital I/O & FRC (clock derived from a
ADCON1 = %00000000 ' dedicated internal oscillator)
CM1CON0=0
CM2CON0=0
TRISC.3 = 0 ' Set RC3 as output port for valve latching solenoid control
Low Valve ' Initialize RC3 (valve) at Low value
TRISA.2 = 1 ' Set RA2 as input port for clock to TMR0
TRISA.3 = 1 ' Set RA3 as input port for sensing METER switch closure
High meter ' Initialize RA2 (meter) at High value for METER pulse inputs
High flush ' Initialize RA3 (flush) at High value for flush interrupt
'Interrupts Settings
FLUSH_INT_FLAG VAR INTCON.0 ' RA3 (FLUSH) On-change-interrupt flag bit
TMRO_INT_FLAG VAR INTCON.2 ' Timer0 overflow flag bit
INTCON = %10101000 ' Enable global, TMR0 & RABIE (RA3 on-change-INT)
IOCA = %00000000 ' Enable RA3 as on-change-INT
'Set INT Handler
ON INTERRUPT GOTO Int_handler
'Start...normal code here
MAIN:
PORTC = %00000000 ' Turn all LEDs off
PAUSE 1
'SLEEP = 65,535 ' Put MC in Sleep state at power up
' Microcontroller is in Sleep State waiting for external FLUSH Interrupt
GOTO Main ' Loop to Main to wait for next Flush interrupt
DISABLE
Int_handler:
IF FLUSH_INT_FLAG = 1 Then ' Interrupt was from RA3 on change
DEFINE WRITE_INT 1
write 9, flush ' Write RA3 (FLUSH) value during testing
PULSOUT valve,1000 ' Generate required 10 msec pulse to RC3 to open valve
High led1 ' Light indicator that valve is open & water flowing
Low low_bat ' Simulate battery monitor input is low
'Put code here to Wakeup the Microcontroller
' Put code here to start a timer to run for 50 secs as a fail safe
' to prevent overflow of toilet tank in case of sensor failure.
'Goto Shutvalve
High flush ' Clear the interrupt
FLUSH_INT_FLAG = 0 ' Clear interrupt flag
Endif
IF TMRO_INT_FLAG = 1 then ' Interrupt was a TMR0 overflow..volume reached
PULSOUT valve,6000 ' Generate required 20 msec pulse to RC3..close valve
WRITE 5, TMR0 ' Write TMR0 value..remove comment for test only
bat_mon = low_bat * Vthr
Write 7, bat_mon ' Remove comment for test only
If bat_mon < Vthr Then
'Light the low battery monitor light
HIGH led2
TMR0 = 256-k ' Reload TMR0 to overflow after k counts
TMRO_INT_FLAG = 0 ' Clear overflow flag
LOW led1
Low led2
RESUME
ENABLE
' If the user program ends by getting to the last statement of the program
' at an END instruction, the MCU will SLEEP and await a wakeup.
Fixed part of the problem
I discovered one of DT's posts that explained part of my problem was that I wasn't properly clearing the mismatch. When I did that the On-interrupt for RA3 worked. However, I noticed in the same DT post his statement "Keep in mind that you will get an interrupt on both the Press and Release of the button. You will eventually need to change the interrupt handler to determine which Edge occurred." I am using a momentary switch button that grounds RA3 for this On-interrupt and now I see happening what he was warning about...I get an intterupt on press AND release. However, I don't quite grasp how to modify my interrupt handler "to determine which Edge occurred." Obviously I want the interrupt to respond only to the press and not the release. Is there a way to filter out the release action to prevent the 2nd interrupt?
Your suggestion solved problem
By following your suggestion for basically debouncing it works. Thanks for advice!;)