View Full Version : How to calculate Burden Resistor ??



andybarrett1
- 12th January 2015, 15:28
Hi thank you for reading.

I have the enclosed circuit using a 100Amp / 5Amp CT ... Bridge Rectified and smoothed.

After searching internet on how to calculate the Burden Resistor I would appreciate some help.

I am looking for 0-10V IP from 0-100Amp


7674

Anybody .....????

Thank You.

MichelJasmin
- 12th January 2015, 20:03
I never used a current transformer but I suggest you place the burden resistor before the bridge.

Then you CT is 100:50 = 20:1

@100A on the primary you'll have 5 amps on the secondary, so 2ohms will give you 10VAC rms.

The bridge has a 1.4V drop you must take in account. Also, AC voltage fully rectified with a capacitor and no load will give you a peak voltage of (v * 1.4142) (1.4142 = square root 2).

So for a 10VDC max:

(10/1.4142) + 1.4 = 8.47VAC on the secondary.

8.47VAC / 5A = 1.694 ohm. Good luck to find one.

My suggestion: pick a standard value < 1.694ohm and then compute the results. Finally, use a good multimeter to caliber your system.

HTH

andybarrett1
- 12th January 2015, 21:11
Thank you for that…

2R is the answer I got to…. I also worked out the Wattage of the resistor needs to be > 50Watt (Large and Hot)

Possible temperature drift !!!!

MichelJasmin
- 13th January 2015, 00:23
Yep! Lot of power! What about shorting the secondary and measuring the current with a current sensor like this:

http://www.allegromicro.com/en/Products/Current-Sensor-ICs/Zero-To-Fifty-Amp-Integrated-Conductor-Sensor-ICs/ACS712.aspx

on a breakout board:

http://www.dx.com/p/acs712-5a-current-sensor-module-blue-206997#.VLRjedKG_CY

[Board Admin: I'm sorry for the ad :frown:, I'm sorry! I'm sorry!]

amgen
- 13th January 2015, 00:46
if you have way to calibrate and check linearity......
7676

andybarrett1
- 13th January 2015, 11:26
Yep! Lot of power! What about shorting the secondary and measuring the current with a current sensor like this:

http://www.allegromicro.com/en/Products/Current-Sensor-ICs/Zero-To-Fifty-Amp-Integrated-Conductor-Sensor-ICs/ACS712.aspx

on a breakout board:

http://www.dx.com/p/acs712-5a-current-sensor-module-blue-206997#.VLRjedKG_CY

[Board Admin: I'm sorry for the ad :frown:, I'm sorry! I'm sorry!]

I like this.....

Also a 30Amp Version.... Might not need a CT !!!

Thank you

andybarrett1
- 13th January 2015, 11:28
Thank you Amgen

Nice Idea.... but pot Wattage needs to be decent size. (More power) ?

amgen
- 13th January 2015, 11:40
ok check these..... http://amploc.com/

andybarrett1
- 13th January 2015, 13:45
Thank you

The sensors all ready exist.. I am attempting to use the output for my purpose.

But will prob look at those in future.

Thank you again

amgen
- 13th January 2015, 20:09
From my experience working with CT's, putting a higher value resister across ct secondary will lower the secondary current by some factor but the voltage still has some relation to the primary current...... that's why a 100 ohm or 1000 ohm resistor will not create that much heat. My guess is that a 100 ohm load resister will probably drop the secondary current to less than 1 amp with 100 amp thru CT.

don