View Full Version : Detecting a pulse



Dennis
- 21st February 2010, 20:18
Hi all

Because of the amount of power failures in our area , I am building a circuit to auto-switch my generator because it's quite a mission getting up at 2am sometimes to go and switch it on when there is a power failure.

I plan to use an opto-isolator initially to detect the power failure however some form of zero-crossing detection may also be a consideration.

This of course raises a good few (maybe silly for some) questions:
1.Which would most accurately detect the pulses ? PULSIN or COUNT? are there other methods?
2.Using either of these does the incoming pulse have to be a known value or can on just check to see if a pulse (ofany/unknown size) exists ?
3.Have I chosen the correct RTC (DS1302) for the job ?

I have been searching the forum for the last few days but haven't qyet found the right example.

I really would appreciate some advice or guidance on how to detect the pulse and absence of a pulse just to get me started.


Kind regards

Dennis

Charles Linquis
- 21st February 2010, 22:25
Use a rectifier (1N4004) and a 10K 2W resistor in series with the LED side of an optoisolator. Put another rectifier across the LED in the reverse direction to protect it against reverse voltage. Connect these across the power line. Put a 10K resistor on the collector of the phototransistor to 5V. The output will be an isolated 50 or 60 Hz square wave.

I would use an interrupt to "watch" this, so your PIC could do other things while watching the power line. Of course the output of the phototransistor will only be LOW for each half-cycle, so if you sampled the phototransistor every 5 ms or so, and it never went low, it would be an idication that the power was "gone'. Note that the rising and falling edges of the square wave will be very close to the zero-crossings of the power line.

Byte_Butcher
- 21st February 2010, 23:31
OK, I gotta be curious... is the whole purpose of this *just* to start a generator?
Do you really need to detect zero crossing and all that?

How about just stepping down the voltage (little transformer), rectifying and putting a small filter cap on the output. Feed it to a PIC pin. If the pin is high... got power. If the pin is low... no power. Poll the pin about once a second should be fine for starting a generator, eh?
Seriously. How quickly do you need to get a generator running? How quickly will it even start? It seems a few seconds delay without power is inevitable if you gotta start an engine.

Of course maybe you have other ideas for this that need the zero crossing anyway?
Just curious...

Heck, I still gotta go out in the rain and put a hand crank on mine to start it. :eek:


steve

http://www.weirdstuffwemake.com/sweetwatergems/geek/images/magicthrob_s015.jpg

Dennis
- 21st February 2010, 23:56
@Steve :-)

That's some Geni , what's the output ? Can't be fun switching it on at 2AM :-)
Mine has electric start :-) will try get a pic up this week for you :-)

Great idea !

I suppose component count and power draw are two reasons why I would go with the sensor.
Searching the forum for lamp-dimmer and mains detect shows huge amounts of info for this kind of thing.
As per quite a few app notes and posts I have seen, a single resistor can be used from LIVE and directly into a PIC pin as a zero-crossing sensor.
OR you can use the opto-isolator.
All that remains then is to check that you are getting a pulse on the pin.
I would like to try the opto-isolator option first but am unsure as to whether to use PULSIN or COUNT (or another method) to check the pulse and what that little line of code should look like.

Kind regards

Dennis

Jerson
- 22nd February 2010, 00:57
I humbly beg to differ here. Why do you even need a PIC to do this? A simple mains rectifier output indicates power present. Similarly, when the power fails, the reservoir capacitor will hold the voltage a little while before indicating mains failure(takes care of short power glitches if you get them)
Sizing this value appropriately can give you some delay before you command the generator to switch on.

In short, mains adaptor -> transistor inverter -> relay is all that is needed to achieve this.

Charles Linquis
- 22nd February 2010, 01:09
Or an AC relay plugged into an outlet!

Dennis
- 22nd February 2010, 01:12
It seems a sentence was left out of my posting!

I wish to log the power failure durations, times and dates as well and that's why I would like to use a PIC as well an an RTC.
The PIC cirucit would either form part of an existing circuit or be battery/solar powered and have little or no draw on my home circuit.

Kind regards
Dennis


Hi all

Because of the amount of power failures in our area , I am building a circuit to auto-switch my generator because it's quite a mission getting up at 2am sometimes to go and switch it on when there is a power failure.

I plan to use an opto-isolator initially to detect the power failure however some form of zero-crossing detection may also be a consideration.

This of course raises a good few (maybe silly for some) questions:
1.Which would most accurately detect the pulses ? PULSIN or COUNT? are there other methods?
2.Using either of these does the incoming pulse have to be a known value or can on just check to see if a pulse (of any/unknown size) exists ?
3.Have I chosen the correct RTC (DS1302) for the job ?

I have been searching the forum for the last few days but haven't yet found the right example.

I really would appreciate some advice or guidance on how to detect the pulse and absence of a pulse just to get me started.


Kind regards

Dennis

Byte_Butcher
- 22nd February 2010, 01:23
Aha!
I figured there must be more to it than just getting the beastie running at 2AM.

Data logging is a good use for a PIC. :)

Just detecting lack of AC power to start a motor is not. :rolleyes:

steve

Byte_Butcher
- 22nd February 2010, 02:18
@Steve :-)
That's some Geni , what's the output ? Can't be fun switching it on at 2AM :-)


6HP @ 650RPM. Aprox 4KW max output and it'll run on just about any flammable liquid you've got. :cool:




Mine has electric start :-)


Yeah, I've heard about guys like you. :p

Maybe electric start for me someday. I've got enough tools and steel to build something for it, but it ain't real high on the priority list.

I don't start it much at 2AM though...
I start at when I get up and kill it when I sleep.
I have enough 12 volt lighting (and big batteries) to get me through the night, and I can always fire up the 1KW inverter if I really need AC at night.


I'd be scared to do any data logging here and find out how many days a year our power is really out.

steve

Dennis
- 22nd February 2010, 20:26
@Steve .. at least you have the geni for those outages :-)

@ any and everyone ... is there really no simple command like
IF PULSE EXIST THEN ... ?

Kind regards

Dennis

timmers
- 22nd February 2010, 20:32
When I worked in Nigeria a few years ago, we employed somebody to start the generator and switch over from utility supply to generator supply. Worked fine, no getting up at 2am like some!

-trouble started when we bought a new generator. We instructed our gen-starter how to check the oil and and where to dip his finger to check the water (couldn't see the level due to the soundproof case).
When we came home later that day, he was busy pouring water into the generator from a watering can. after his second refill I became curious as to why the generator was needing so much water, and there on the top of the case, was the oil filler cap as another 2 gallons disappeared down to the depths of our brand new generator. When I pulled the dipstick out, a spout of water flowed.

After that episode I sacked the gen-starter and I built a PIC based auto starter, which would check the incoming 3 phase for over volts (occaisionaly), under volts (often), one or all phases missing (very common) and then switch over as required. It had a variable brown out facility to prevent reccuring start / stop and control of other variables like cranking time out and cool down runs. It even switched the contactor from utility to local automatically. It used 3x opto couplers to monitor the 3 phases and 3 relays for run, glow & crank.

Worked a treat!

Dennis
- 22nd February 2010, 20:56
@trimmers
That definitely is a classic :-)
So the initial code would have been something like

If water_level exist then
goto sack_gen_starter
else goto use_PIC
end if

Thanks for the info

Dennis

WOZZY-2010
- 23rd February 2010, 13:23
Other fun and useful stuff that might be added, with various levels of cost and complexity:


Log generator run time
Monitor / Alarm fuel level
Monitor /Alarm engine or generator winding temperatures
Count power outage events / Log power out time
Monitor output power or voltage and current demand
Auto start periodically to maintain bearings and equipment health...alarm if no start
etc ...


This is what I love about the versatility of using PIC chips.

Dennis
- 23rd February 2010, 20:10
@WOZZY-2010 yes plenty that can be added.
Hardest part would be getting a fuel top up :-)

OK so still no replies regarding a simple IS PULSE EXISTS command ?
I can easily detect zero-crossing but need to know how to check for th
I was thinking of just checking for an absolute minimum pulse using PULSIN or use COUNT since AC has a 50% duty cycle and I would be checking a frequency of 50Hz or 60Hz but how do I set the period to be infinite ?
Using this approach I could say something like WHILE COUNT_VAR > 1

So here are the questions ?

1. Can COUNT period be set to inifinity ?
2. Can COUNT be set to a tight loop to count mains pulses so a variable always stays high so that I could say something like IF COUNT >1 THEN AC EXISTS ?
3. If I used and interrupt on change for every zero-crossing could the interrupt be checked ..something like if interrupt exists then ... or if no interrupt exists then ...

Any thoughts/ideas are welcome ?

Kind regards

Dennis

Charles Linquis
- 23rd February 2010, 20:45
Again - I don't know what else your PIC must do at the same time, but PULSIN and COUNT are generally bad, since your code can do NOTHING ELSE during the count interval.

If that is the case just do something like:




CLEAR

Topp:

IF InputPin = 0 THEN
Counter = 0
ENDIF

IF Counter > 2 then goto PowerGone
IF Counter < 254 THEN Counter = Counter + 1
Pause 5
Goto Topp


PowerGone:
HSEROUT ["Turn on the Generator"]
Pause 10
END

Dennis
- 23rd February 2010, 22:38
@Charles

Thanks very much for both replies and apologies for not replying tot he first one, I think for some reason I got sidetracked after reading it (it suddenly got some thoughts going) and I forgot to reply :-(

Regarding the latest posting you have made... what exactly do you have in mind with this code ?

IF InputPin = 0 THEN
Counter = 0
ENDIF

IF Counter > 2 then goto PowerGone
IF Counter < 254 THEN Counter = Counter + 1
Pause 5
Goto Topp


Are you suggesting I have a zero-cross detector on 'InputPin' ?

And Counter > 2 ?
What are we counting ?


Kind regards
Dennis

Charles Linquis
- 23rd February 2010, 23:47
There are dozens of ways to do this, but in this case, I'm referring to the circuit that I described earlier - an optoisolator. The input pin in my code would be connected to the collector of the phototransistor in the optocoupler. If you build the circuit I described, you will find that the output of the opto is a square wave, with a period equal to the period of your AC (60 Hz = 16.666 ms, 50Hz = 20 ms). The output will be low for one half-cycle (8.3ms or 10 ms) and high for the other half-cycle. The low-to-high and high-to-low transitions will occur on the zero-crossings of the AC. The circuit only detects "positive" half-cycles.

The counter increments every 5 msec, but if a half cycle comes along, the counter gets cleared (because the pin is low), and the count never gets above 2. If a positive half-cycle is missing, the counter increments to 3 and you get an indication that your power is gone.



PULSIN and COUNT are sometimes called "blocking" commands because between the invocation of the command and the timeout, the code can do nothing else. I generally avoid them at all costs.

Dennis
- 28th February 2010, 13:12
@ Charles

Once again thanks for the reply ...!

Will feedback once I have something functional :-)

Kind regards

Dennis