    I have a HTC4067 16x1 multiplexer, it's controlled by four lines S0, S1, S2, S3
    I have these all connected to Port B pins 4,5,6,7 respectively on my pic. This could be reversed to 7,6,5,4 if that helps.
    I'm after ideas on how to step through the input options 0-15 as per the truth table below as efficiently as possible.

    i.e. select input 0, then 1, then 2 etc etc in sequence..

    Increment a byte from 0 to 15 and mask off the 4 high bits?

    Ideally I don't want to effect the output/status etc on the PortB 0,1,2,3 during this operation..

    Name:  HTC4067TruthTable.jpg
Views: 683
Size:  57.0 KB
    Last edited by retepsnikrep; - 19th July 2018 at 09:38.

  2. #2
    Join Date
    Sep 2009
    Posts
    737


    Did you find this post helpful? Yes | No

    Default Re: Multiplexer address control..

    If you are using PIC 18F, then use simplest solution is
    LATB.4=Control.0
    LATB.5=Control.1
    LATB.6=Control.2
    LATB.7=Control.3

    EDIT:
    For PIC16

    PortBCopy var byte

    PortBCopy = PORTB
    PortBCopy .4=Control.0
    PortBCopy .5=Control.1
    PortBCopy .6=Control.2
    PortBCopy .7=Control.3
    PORTB=PortBCopy

  3. #3


    Did you find this post helpful? Yes | No

    Default Re: Multiplexer address control..

    Yes thanks, but how to step through the options in the most efficient way without disturbing ports B0-3

  4. #4
    Join Date
    Sep 2009
    Posts
    737


    Did you find this post helpful? Yes | No

    Default Re: Multiplexer address control..

    for control = 0 to 15
    LATB.4=Control.0
    LATB.5=Control.1
    LATB.6=Control.2
    LATB.7=Control.3
    next control

  5. #5
    Join Date
    Aug 2003
    Posts
    985


    Did you find this post helpful? Yes | No

    Default Re: Multiplexer address control..

    It would be quicker if you used the port bits 0-3 instead, so you could just increment the port b value.
    The quickest way also depends where the enable bit is connected.

  6. #6
    Join Date
    Mar 2003
    Location
    Commerce Michigan USA
    Posts
    1,166


    Did you find this post helpful? Yes | No

    Default Re: Multiplexer address control..

    Pedja089, In your suggested code you are treating "Control" as an array. If it is not then you are just resetting the LATx bits 16 times.
    Dave Purola,
    N8NTA
    EN82fn

  7. #7
    Join Date
    Sep 2009
    Posts
    737


    Did you find this post helpful? Yes | No

    Default Re: Multiplexer address control..

    I'm using as single bit, not array. And changing only upper 4 bit.
    For this PBP will generate 4 asm instruction per PBP line, and execute 2 or 3 of them.
    In worst case scenario 12 asm instruction are executed.
    Compared to any PBP math function size, and speed are better in this case.
    Maybe using logic you can get same result. You can try it if you want.
    Let me explain little more...
    Control=2
    LATB.4=Control.0
    LATB.5=Control.1
    LATB.6=Control.2
    LATB.7=Control.3
    Bit 4 of LAT register is set to 0, bit 5 of LAT register is set to 1, bits 6,7 of LAT register is set to 0.
    Bits 0,1,2,3, are unaffected.


    PS
    Array would be Control[i]...

  8. #8
    Join Date
    Mar 2003
    Location
    Commerce Michigan USA
    Posts
    1,166


    Did you find this post helpful? Yes | No

    Default Re: Multiplexer address control..

    Pedja089, Why not just say:

    for control = 0 to 15
    LATB = LATB & $0F 'strip upper 4 bits
    LATB = LATB | Control << 4 'add new control bits
    next control
    Dave Purola,
    N8NTA
    EN82fn

  9. #9
    Join Date
    Sep 2009
    Posts
    737


    Did you find this post helpful? Yes | No

    Default Re: Multiplexer address control..

    Because that would generate more than double ASM instructions. Lets compare ASM for your code and mine.

    Here is your code
    Code:
    LATB = LATB & $0F 'strip upper 4 bits
    LATB = LATB | Control << 4 'add new control bits
    compiled:
    Code:
                Line         Address         Opcode         Label         DisAssy    
                   468            03A6           0E0F           Z00039         MOVLW 0xF      
                   469            03A8           168A                          ANDWF LATB, F, ACCESS
                   470            03AA           C03D           Z0003A         MOVFF Control, R0 
                   471            03AC           F013                          NOP            
                   472            03AE           6A14                          CLRF 0x14, ACCESS
                   473            03B0           6A15                          CLRF 0x15, ACCESS
                   474            03B2           6A16                          CLRF 0x16, ACCESS
                   475            03B4           0E04                          MOVLW 0x4      
                   476            03B6           DEAE                          RCALL SHIFTL   
                   477            03B8           6E23                          MOVWF 0x23, ACCESS
                   478            03BA           C014                          MOVFF 0x14, 0x24
                   479            03BC           F024                          NOP            
                   480            03BE           C015                          MOVFF 0x15, 0x25
                   481            03C0           F025                          NOP            
                   482            03C2           C016                          MOVFF 0x16, 0x26
                   483            03C4           F026                          NOP            
                   484            03C6           5023                          MOVF 0x23, W, ACCESS
                   485            03C8           128A                          IORWF LATB, F, ACCESS
    If you look close there is RCALL SHIFTL.
    Code for that:
    Code:
                         Line         Address         Opcode         Label         DisAssy    
                   139            0114           0FFF           SHIFTL         ADDLW 0xFF     
                   140            0116           E2F9                          BC shiftlloop  
                   141            0118           5013                          MOVF R0, W, ACCESS
                   142            011A           EF8E                          GOTO 0x31C     
                   143            011C           F001                          NOP
    Then there is GOTO 0x31C
    Code for that:
    Code:
                         Line         Address         Opcode         Label         DisAssy    
                   399            031C           0100           DUNN           MOVLB 0x0      
                   400            031E           0000           DUNN5          NOP            
                   401            0320           0012                          RETURN 0
    Then there is also BC shiftlloop
    Code:
                       Line         Address         Opcode         Label         DisAssy    
                   134            010A           90D8           shiftlloop     BCF STATUS, 0, ACCESS
                   135            010C           3613                          RLCF R0, F, ACCESS
                   136            010E           3614                          RLCF 0x14, F, ACCESS
                   137            0110           3615                          RLCF 0x15, F, ACCESS
                   138            0112           3616                          RLCF 0x16, F, ACCESS
                   139            0114           0FFF           SHIFTL         ADDLW 0xFF     
                   140            0116           E2F9                          BC shiftlloop  
                   141            0118           5013                          MOVF R0, W, ACCESS
                   142            011A           EF8E                          GOTO 0x31C     
                   143            011C           F001                          NOP
    My code:
    Code:
    LATB.4=Control.0
    LATB.5=Control.1
    LATB.6=Control.2
    LATB.7=Control.3
    Compiled:
    Code:
                         Line         Address         Opcode         Label         DisAssy    
                   458            0392           B035           Z00039         BTFSC Control, 0, ACCESS
                   459            0394           888A                          BSF LATB, 4, ACCESS
                   460            0396           A035                          BTFSS Control, 0, ACCESS
                   461            0398           988A                          BCF LATB, 4, ACCESS
                   462            039A           B235           Z0003A         BTFSC Control, 1, ACCESS
                   463            039C           8A8A                          BSF LATB, 5, ACCESS
                   464            039E           A235                          BTFSS Control, 1, ACCESS
                   465            03A0           9A8A                          BCF LATB, 5, ACCESS
                   466            03A2           B435           Z0003B         BTFSC Control, 2, ACCESS
                   467            03A4           8C8A                          BSF LATB, 6, ACCESS
                   468            03A6           A435                          BTFSS Control, 2, ACCESS
                   469            03A8           9C8A                          BCF LATB, 6, ACCESS
                   470            03AA           B635           Z0003C         BTFSC Control, 3, ACCESS
                   471            03AC           8E8A                          BSF LATB, 7, ACCESS
                   472            03AE           A635                          BTFSS Control, 3, ACCESS
                   473            03B0           9E8A                          BCF LATB, 7, ACCESS
    in my code there is only 16 instruction. In worst case 12 is executed, in best case 8.
    Can you calculate best and worse case for your code? Then compare it
    This is depends lot of internal PBP optimization, and lib structure.
    Another example is to use nested IFs instead of AND. Also I found way to use some temporally variable and single condition IF, and to get complex IFs that are fraction of size PBP's single line IF with multiple condition.
    There is somewhere example on forum.
    Same apply to math formula, tend to use single operation per line, and multiple lines...
    Then compiler doesn't have to store bunch or intermediate results.
    Sometimes less is more, and more is less.

    If you write more lines of simple code then compiler have less to do. And tend to get better result(smaller code, less ram for lib's, faster execution times)

    EDIT:
    I'm using long, so there is little overhead like this
    472 03AE 6A14 CLRF 0x14, ACCESS
    473 03B0 6A15 CLRF 0x15, ACCESS
    474 03B2 6A16 CLRF 0x16, ACCESS
    to clear rest of R0 internal register.
    Last edited by pedja089; - 23rd July 2018 at 11:07.

  10. #10
    Join Date
    Mar 2003
    Location
    Commerce Michigan USA
    Posts
    1,166


    Did you find this post helpful? Yes | No

    Default Re: Multiplexer address control..

    I didn't know we were going for speed....
    Dave Purola,
    N8NTA
    EN82fn

  11. #11
    Join Date
    May 2013
    Location
    australia
    Posts
    2,379


    Did you find this post helpful? Yes | No

    Default Re: Multiplexer address control..

    or even this way, constant speed

    Code:
    control        EQU  0x30
    latb_shadow    EQU  0x31
    LATCH          EQU  0x32   ; simulate lat reg
     
    
     ORG     ResetVector
     goto    Start
    
    
    Start
      MOVLW 0
      MOVWF control
      MOVLW 3
      MOVWF LATCH ; eg. LATB,A
    lopo
      BANKSEL latb_shadow
      INCF control,F
      MOVLW 0xf
      ANDWF control,F
      
      MOVFF LATCH ,latb_shadow 
      MOVLW 0xf
      andwf latb_shadow ,F  
      SWAPF latb_shadow,F 
      MOVF  control,W
      IORWF latb_shadow ,F
      SWAPF latb_shadow,W
      MOVWF LATCH 
     
      GOTO lopo
    
      END
    Warning I'm not a teacher

  12. #12
    Join Date
    May 2013
    Location
    australia
    Posts
    2,379


    Did you find this post helpful? Yes | No

    Post Re: Multiplexer address control..

    A little more thought reduces it further,no need at all for a shadow working reg at all
    works perfectly on the simulator steps through all 16 "control" states on latb 4-7 and preserves latb 0-3.

    Code:
    ; TODO INSERT CONFIG CODE HERE USING CONFIG BITS GENERATOR
      Processor      18f4550
     
      
      include         "p18f4550.inc"   
    TRUE  equ 1
    FALSE  equ 0
     cblock 0x30 
    control     
    ;latb_shadow   
     endc    
     
     
    RES_VECT  CODE    0x0000            ; processor reset vector
        GOTO    START                   ; go to beginning of program
    ; TODO ADD INTERRUPTS HERE IF USED
    MAIN_PROG CODE                      ; let linker place main program
    START
       
    
     
    
    
    
      MOVLW 0f
      MOVWF control
      MOVLW 3
      MOVWF  LATB,A
    lopo
      BANKSEL control
      INCF control,F
      MOVLW 0xf
      ANDWF control,F
      
      
      MOVF LATB,A,W
      ANDLW 0XF
      SWAPF WREG,F
      IORWF control,W
      SWAPF WREG,F
      MOVWF LATB ,A
     
      GOTO lopo
    Last edited by richard; - 24th July 2018 at 09:02.
    Warning I'm not a teacher

  13. #13
    Join Date
    Aug 2005
    Location
    Michigan, USA
    Posts
    224


    Did you find this post helpful? Yes | No

    Default Re: Multiplexer address control..

    if I may...

    Code:
    RES_VECT  CODE    0x0000            ; processor reset vector
        GOTO    START                   ; go to beginning of program
    ; TODO ADD INTERRUPTS HERE IF USED
    MAIN_PROG CODE                      ; let linker place main program
    START
     
    
            MOVLW   0f
            MOVWF   control
            MOVLW   3
            MOVWF   LATB,A
    lopo
            BANKSEL control
            incf    control,F       ; control = control + 1
            bcf     control,4       ; control = control mod 15
      
            swapf   control,W       ; B7..B4 <- control
            xorwf   LATB,W          ; wreg = differences
            andlw   0xF0            ; ignore B3..B0 bits
            xorwf   LATB,F          ; update B7..B4 bits
     
            GOTO    lopo

  14. #14
    Join Date
    Aug 2005
    Location
    Michigan, USA
    Posts
    224


    Did you find this post helpful? Yes | No

    Default Re: Multiplexer address control..

    t'would be simpler/faster still if you were to use the B3..B0 pins as both the 'control' variable and 'control' I/O;

    Code:
    RES_VECT  CODE    0x0000            ; processor reset vector
        GOTO    START                   ; go to beginning of program
    ; TODO ADD INTERRUPTS HERE IF USED
    MAIN_PROG CODE                      ; let linker place main program
    START
     
    
            movlw   0x30            ; B7..B4 other I/O, B3..B0 = control
            movwf   LATB            ;
    lopo
            incf    LATB,W          ; B3..B0 bits = control, 0..15
            xorwf   LATB,W          ; wreg = differences
            andlw   0x0F            ; ignore B7..B4 bits (and control mod 16 for free)
            xorwf   LATB,F          ; update B3..B0 bits, 0..15
     
            GOTO    lopo
    Last edited by Mike, K8LH; - 25th July 2018 at 00:08.

  15. #15
    Join Date
    May 2013
    Location
    australia
    Posts
    2,379


    Did you find this post helpful? Yes | No

    Default Re: Multiplexer address control..

    if I may...
    Mike, K8LH
    that's exactly what a good forum needs

    your solution is excellent
    Warning I'm not a teacher

  16. #16
    Join Date
    Aug 2005
    Location
    Michigan, USA
    Posts
    224


    Did you find this post helpful? Yes | No

    Default Re: Multiplexer address control..

    I like pedja089's solution which is probably about as simple, efficient, and elegant as you can get with pure PBP code. He might test clearing the four LATB bits and then setting them based on if control.0 = 1 then latb.4 = 1 (or something similar).

    I have to say the code PBP generated for the "Control << 4" instruction was pretty dismal. I'm curious to see what XC8 will generate for that...
    Last edited by Mike, K8LH; - 25th July 2018 at 05:13.

  17. #17
    Join Date
    May 2013
    Location
    australia
    Posts
    2,379


    Did you find this post helpful? Yes | No

    Default Re: Multiplexer address control..

    I like pedja089's solution which is probably about as simple, efficient, and elegant as you can get with pure PBP code
    it is simple but I wonder if it may cause some analog channel crosstalk effects when control inputs are changed sequentially like that esp at low clock speeds , just a thought.
    Warning I'm not a teacher

  18. #18
    Join Date
    Aug 2005
    Location
    Michigan, USA
    Posts
    224


    Did you find this post helpful? Yes | No

    Default Re: Multiplexer address control..

    Oops! I didn't think of that...

Similar Threads

  1. Replies: 5
    Last Post: - 21st January 2014, 17:10
  2. How do I give a radio control car autonomous control
    By Kenjones1935 in forum General
    Replies: 190
    Last Post: - 17th January 2010, 16:40
  3. Multiplexer channel selection
    By Castor in forum mel PIC BASIC Pro
    Replies: 17
    Last Post: - 19th May 2008, 11:51
  4. Using a MAX7219 (LED digit multiplexer) with a 16F88
    By flotulopex in forum mel PIC BASIC Pro
    Replies: 8
    Last Post: - 11th March 2007, 22:11

Members who have read this thread : 1

You do not have permission to view the list of names.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts