    I want to use 75176 for RS 485 network with over 50 devices. However it is mentioned that the maximum devices i can connect in a network is 32. Is it possible to increase the number to more than 32 ?

    Thanks
    Cheers,

    mychangl
    "The Dream Is Everything"

  2. #2
    Join Date
    Nov 2008
    Posts
    48


    Did you find this post helpful? Yes | No

    Default

    We use as address header in our protocol one byte, so you have a range of 256 devices.
    Normaly you specify the high-nibble for the device class, the lower-nibble for the device address range.
    For example unit-type 1 has A0h - AFh, unit-type 2 has B0h-BFh and so on.
    Regards,
    Ralf

  3. #3
    Join Date
    Dec 2005
    Posts
    1,073


    Did you find this post helpful? Yes | No

    Default

    Older RS485 driver ICs (e.g. 75176) can only do 32. Newer drivers (e.g. ST485) can do as many as 256.

  4. #4
    Join Date
    Nov 2003
    Location
    Greece
    Posts
    3,807


    Did you find this post helpful? Yes | No

    Default

    check the data sheets of the device you will use. If the input of the RS-485 receiver puts high load on the lines then node number is limited (up to 32 for the RS-485 specs).

    Newer devices like form analog devices (http://www.analog.com/en/interface/r...cts/index.html) present minimum load on the lines so up to 256 nodes can be implemented.

    Ioannis

  5. #5
    Join Date
    Nov 2008
    Posts
    48


    Did you find this post helpful? Yes | No

    Default

    Ah, sorry, was a misunderstanding from me,
    thoght you have restrictions with the addresses...

  6. #6
    Join Date
    Jun 2006
    Posts
    40


    Did you find this post helpful? Yes | No

    Default

    Thanks for the information. Get better understanding.
    1. If i still use 75176, do you think the attach circuit will work ?

    2. Do you think if should isolate the line as in the attachment if the wiring goes so long ? ( could have trouble with terminal resistance or isolation of fault )

    3. Most of the articles i gone through does not mention the actual type of cable to be used except twisted pair. In order to determine terminal resistor value, i need to know the cable impedance. What if i do not have the information ? Will 120ohm resistor still helps. Or it is better to use 120 ohm with shorter distant cable but i can add isolator to extend the communication line ?
    Cheers,

    mychangl
    "The Dream Is Everything"

Similar Threads

  1. RF sensor network
    By Ron Marcus in forum mel PIC BASIC Pro
    Replies: 10
    Last Post: - 21st September 2006, 00:07
  2. RS 485 wireless communication
    By Armadus in forum mel PIC BASIC Pro
    Replies: 22
    Last Post: - 26th January 2006, 19:30
  3. RS485 - ibutton network
    By ccsparky in forum mel PIC BASIC Pro
    Replies: 7
    Last Post: - 6th June 2005, 21:48
  4. Slave Databuffer - RS-485 network
    By DynamoBen in forum mel PIC BASIC Pro
    Replies: 4
    Last Post: - 1st June 2005, 18:36
  5. RS 485 using 16F84A
    By ngeronikolos in forum mel PIC BASIC Pro
    Replies: 1
    Last Post: - 18th May 2005, 14:46

Members who have read this thread : 1

You do not have permission to view the list of names.

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts