I want to use 75176 for RS 485 network with over 50 devices. However it is mentioned that the maximum devices i can connect in a network is 32. Is it possible to increase the number to more than 32 ?
Thanks
I want to use 75176 for RS 485 network with over 50 devices. However it is mentioned that the maximum devices i can connect in a network is 32. Is it possible to increase the number to more than 32 ?
Thanks
Cheers,
mychangl
"The Dream Is Everything"
We use as address header in our protocol one byte, so you have a range of 256 devices.
Normaly you specify the high-nibble for the device class, the lower-nibble for the device address range.
For example unit-type 1 has A0h - AFh, unit-type 2 has B0h-BFh and so on.
Regards,
Ralf
Older RS485 driver ICs (e.g. 75176) can only do 32. Newer drivers (e.g. ST485) can do as many as 256.
check the data sheets of the device you will use. If the input of the RS-485 receiver puts high load on the lines then node number is limited (up to 32 for the RS-485 specs).
Newer devices like form analog devices (http://www.analog.com/en/interface/r...cts/index.html) present minimum load on the lines so up to 256 nodes can be implemented.
Ioannis
Ah, sorry, was a misunderstanding from me,
thoght you have restrictions with the addresses...
Thanks for the information. Get better understanding.
1. If i still use 75176, do you think the attach circuit will work ?
2. Do you think if should isolate the line as in the attachment if the wiring goes so long ? ( could have trouble with terminal resistance or isolation of fault )
3. Most of the articles i gone through does not mention the actual type of cable to be used except twisted pair. In order to determine terminal resistor value, i need to know the cable impedance. What if i do not have the information ? Will 120ohm resistor still helps. Or it is better to use 120 ohm with shorter distant cable but i can add isolator to extend the communication line ?