    Default Re: PID-filter routine (2nd try).

    Hi,
    1) That is indeed an issue with the example code which went unobserved for a very long time, someone noticed it and mentioned it a couple of posts back in the thread. Unfortunately the forum doesn't allow me to fix it in the original post. Anyway, you are 100% right, if you're using the HPWM command then you should set the output clamp to 255. With that said the standard CCP module creating the PWM output can provide resolution of up to 10bits depending on frequency, you just can't "access" it using the HPWM command.

    2) Sounds like a good start. Getting the tuning values right can be tricky, especially so on slow systems since it takes so damn long to see if you got it right or not. I expect this particular "plant" to be extra tricky due to the somewhat unrepeatable/unpredictable "performance" of a charcoal bed - I imagine.

    One thing you might consider is to run the heater/fan/furnace whatever "open loop" until the temperature starts to approach the setpoint and only then switch on the PID. A more elegant but also a bit more complicated way is to create a ramping action in a way that the setpoint, instead of being bumped from ambient to "working temp" is ramped up at a rate that the "plant" can actually follow.

    If you're concerned that a dutycycle of 0% won't provide enough oxygen to keep the fire alive then simply don't allow it to go below a certain value to keep the fan running at all times.

    /Henrik.

  2. #2
    Join Date
    Jan 2012
    Location
    Grid EN19MV
    Posts
    159


    Did you find this post helpful? Yes | No

    Default Re: PID-filter routine (2nd try).

    Quote Originally Posted by HenrikOlsson View Post
    Hi,

    One thing you might consider is to run the heater/fan/furnace whatever "open loop" until the temperature starts to approach the setpoint and only then switch on the PID. A more elegant but also a bit more complicated way is to create a ramping action in a way that the setpoint, instead of being bumped from ambient to "working temp" is ramped up at a rate that the "plant" can actually follow.
    I had actually planned to run the fan in manual mode until I am near the setpoint, then allow the PID loop to take over in auto mode.

    The other question I had is on the reset. In the example, it is set to .5. What causes the integral ramp to get steeper? Would that be an increase in the number? What kind of range of numbers are you expecting on the reset .1 to 1 or even higher than that?

    BTW, while running it in simulation last night, I discovered that a derivative of 0 causes unpredictable results - to remove the derivative, you have to set it to 1.

    In my reading and conversations with people who deal with PID (one of which was an instructor at a local community college) I am told that temperature control only requires process and integral, not derivative.

    Thanks again,

    Andy
    Last edited by andywpg; - 17th April 2013 at 14:28. Reason: Added info
    "I have noticed that even those who assert that everything is predestined and that
    we can change nothing about it still look both ways before they cross the street"


    -Stephen Hawking

  3. #3
    Join Date
    Jan 2012
    Location
    Grid EN19MV
    Posts
    159


    Did you find this post helpful? Yes | No

    Default Re: PID-filter routine (2nd try).

    If anyone is interested, here is what I used to run the simulation (my controller has an LCD)

    Code:
    #CONFIG
     __config _CONFIG1, _INTRC_OSC_NOCLKOUT & _WDT_OFF & _MCLRE_OFF & _LVP_OFF & _CP_OFF 
    #ENDCONFIG
    
    DEFINE OSC 8  'LETS PBP KNOW THE OSCILLATOR IS RUNNING AT 8MHz
    DEFINE NO_CLEARWDT 1 'NO WATCHDOG TIMER - FOR NOW - WILL DO OUR OWN CLRWDT
    
    
    OSCCON = %01110001 '8 MHz INTERNAL OSCILLATOR, INTERNAL OSCILLATOR IS USED FOR SYSTEM CLOCK
    
    
    DISABLE 'NO PBP INTERRUPTS NO PBP DEBUG
    
    ' Set LCD Data port
    DEFINE LCD_DREG PORTB
    ' Set starting Data bit (0 or 4) if 4-bit bus
    DEFINE LCD_DBIT 0
    ' Set LCD Register Select port
    DEFINE LCD_RSREG PORTB
    ' Set LCD Register Select bit
    DEFINE LCD_RSBIT 4
    ' Set LCD Enable port
    DEFINE LCD_EREG PORTB
    ' Set LCD Enable bit
    DEFINE LCD_EBIT 5
    ' Set LCD bus size (4 or 8 bits)
    DEFINE LCD_BITS 4
    ' Set number of lines on LCD
    DEFINE LCD_LINES 2
    ' Set command delay time in us
    DEFINE LCD_COMMANDUS 1500
    ' Set data delay time in us
    DEFINE LCD_DATAUS 44
    
    
    
      '// Set up hardware registers, ADC etc here (not shown) //
    
      ADValue VAR WORD                     '<---This is your variable.
      SetPoint VAR WORD                    '<---This is your variable.
      COUNTER VAR BYTE
      RUN_IND VAR BYTE
    
    
    
    
      INCLUDE "incPID.pbp"                 'Include the PID routine.
    
        'These variables are declared by the incPID routine but
        'the user needs to assign values to them.
        pid_Kp = $0700                     'Set Kp to 7.0 GAIN
        pid_Ki = $0080                     'Set Ki to 0.5 RESET
        pid_Kd = $0001                     'Set Kd to 0 (Derivative not necessary)
        pid_Ti = 8                         'Update I-term every 8th call to PID
        pid_I_Clamp = 100                  'Clamp I-term to max ±100
        pid_Out_Clamp = 255                'Clamp the final output to 0 to 255
    	Setpoint = 230		               '<---Set desired position.
    	RUN_IND = 1
    
    START:
       	FOR ADVALUE = 225 TO 235 'TEST A BUNCH OF VALUES
    		FOR COUNTER = 1 TO 10
       			pid_Error = Setpoint - ADValue     'Calculate the error
    			Gosub PID                          'Result returned in pid_Drive
       			if pid_Out.15 then pid_out = 0     'IF NEGATIVE THEN SHUT OFF FAN
       			pid_Out = ABS pid_Out              'Convert from two's comp. to absolute
    '  			HPWM 1, pid_Out, 10000             'Set PWM output
    
    			LCDOUT $FE, 1, "AD=", DEC ADVALUE, " PO=", SDEC PID_OUT
    			LCDOUT $FE, $C0, "RUN #", DEC COUNTER, " SETP ", DEC SETPOINT
    			Pause 1000                           'Wait....
    		NEXT COUNTER
    	NEXT ADVALUE
    	IF RUN_IND = 1 THEN
    		RUN_IND = 0 
    		GOTO START 'DO IT AGAIN SO THAT ITS AS IF THE TEMPERATURE DROPPED 
    	ENDIF
    	LCDOUT $FE, 1, "DONE!"
    	DO
    	LOOP 'ENDLESS LOOP
    	
    END
    Last edited by andywpg; - 17th April 2013 at 14:51.
    "I have noticed that even those who assert that everything is predestined and that
    we can change nothing about it still look both ways before they cross the street"


    -Stephen Hawking

  4. #4
    Join Date
    Oct 2005
    Location
    Sweden
    Posts
    3,522


    Did you find this post helpful? Yes | No

    Default Re: PID-filter routine (2nd try).

    Hi,
    I'm sure you're correct that you don't need derivative. I'm surprised though that you get unpredictable results when you set it to zero, I'll have to look into that. What exactly is it doing?
    Anyway setting it to 1 is pretty close to 0 (1/256 to be precise.) So it shouldn't have any effect on the actual control loop in your case.

    The PID_Ki isn't the "reset time" (at least I don't think it's comparable to that), it's the integral gain. To get more integral action (steeper ramp) you increase the gain.

    Here's how it works, basically:
    Each time you GOSUB PID the integral term takes the error and adds it to an accumulator. It then increments a counter and compares the counter value to PID_Ti, if the counter value is less than PID_Ti it's done. If the counter is equal to PID_Ti it takes the (value in the accumulator) * (integral gain/256) / PID_Ti, it then adds the result to the output and resets the accumulator as to not overflow it. I think you can compare the PID_Ti value to what's sometimes called "reset time". (It does a couple of other things as well but lets not go into that right now).

    As to a range of values for the integral gain..... all I can say really is that it's usually a lot less than the proportional gain, which in turn is usually a lot less than the derivative gain (which you don't use here).

    Hope it helps.
    /Henrik.
    Last edited by HenrikOlsson; - 17th April 2013 at 18:00.

  5. #5
    Join Date
    Jan 2012
    Location
    Grid EN19MV
    Posts
    159


    Did you find this post helpful? Yes | No

    Default Re: PID-filter routine (2nd try).

    Quote Originally Posted by HenrikOlsson View Post
    Hi,
    I'm sure you're correct that you don't need derivative. I'm surprised though that you get unpredictable results when you set it to zero, I'll have to look into that. What exactly is it doing?
    All this was observed using the code I posted above.

    With the derivative set to one, and the loop at 216 (degrees) it usually starts with an output to the PWM of 150 or so. As the sample gets closer to the setpoint (230) it ramps down - as it should.

    With derivative set to 0, the PWM starts at about 20, and goes down from there - I can't remember exactly where, but at some point (long before its at the setpoint) its at ZERO - with a charcoal fire, that means its never getting to the setpoint. Strangely enough, on the SECOND run through the numbers, it starts working properly - not sure why. Maybe its my fault.

    It seems to work great with the derivative set to 1, though, acts exactly as it should.


    Quote Originally Posted by HenrikOlsson View Post
    Hope it helps.
    Very much so. Now, if only this damn snow would go away........

    Thanks again,

    Andy
    Last edited by andywpg; - 18th April 2013 at 00:15. Reason: spelling
    "I have noticed that even those who assert that everything is predestined and that
    we can change nothing about it still look both ways before they cross the street"


    -Stephen Hawking

Similar Threads

  1. Darrel's latest 16 bit averaging routine?
    By jellis00 in forum mel PIC BASIC Pro
    Replies: 9
    Last Post: - 17th October 2009, 01:57
  2. 2nd order Low-pass passive RC filter on PWM
    By munromh in forum mel PIC BASIC Pro
    Replies: 6
    Last Post: - 29th January 2009, 19:03
  3. Atod Digital Filter
    By GeoJoe in forum mel PIC BASIC Pro
    Replies: 3
    Last Post: - 2nd April 2008, 17:04
  4. PID controller in 16F737
    By joeri in forum mel PIC BASIC
    Replies: 8
    Last Post: - 24th June 2006, 11:39
  5. 2nd Order Digital Filter for 24-bit
    By sefayil in forum mel PIC BASIC
    Replies: 0
    Last Post: - 2nd December 2005, 21:55

Members who have read this thread : 3

You do not have permission to view the list of names.

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts