Try this way.
1. The zero crossing is where the triac turns off.
2. You need the period between 2 zero crossings to decide the time after the zero crossing you need to turn ON the triac
3. Depending on the amount of power you need to output, you need to turn on the triac that much earlier than the zero crossing.
The period is 10mS for a half period of 50Hz,
if you need 50% power, you need to turn on your triac 5mS after the zero crossing.
if you need 25% power, you will turn on the triac 10-2.5ms = 7.5mS after the zero crossing.
for 10% power, you will turn on the triac 10-1mS = 9mS after the zero crossing.
I hope I was able to communicate clearly without using a diagram.
Cheers